LED Panel Lights
Tim Ganz
Dec 2010
Dallas, Texas
704
Who makes the best LED panel lights? I use Hoffman enclosures but the LED lights from Hoffman don't look to be built all that well. Anyone have a favorite?
Also what is the best method to set these up where you can have lights even when the 480 is off? I would like to use 24vdc lighting units.
I use automation direct for most things like that.
As far as when the 480 is off, you would need a separate power supply for your control voltage. Some people frown on this because the one switch doesn't kill all power to the cabinet.
If you really want lights with the power off, I believe Banner has some nice battery powered LED panel lights. You can mount them permanently or magnetic so you can move them around. I can't vouch for battery life, but I have a battery operated LED tap light at home that is past 5 years on the original AA batteries. I only use it during power failures.
I did not know they had battery lights. Banner has a good selection. I have been using them for a while and they work great.
Tim,
FYI, control voltages above 120 vac is not allowed in control panels unless built years ago per nfpa 79 - Electrical standard for industrial machinery.
motor wiring is obviously more than 120.
also, you must look at the environment you are putting lights, photos, limit switches in. are these devics rated for the area?
you MUST also place a placard on the enclosure door stating that there is secondary power in place even when the main disconnect is off.
regards,
james
Tim,
regards,
james
Can you cite the section of NFPA 79 that states this? I have machines here that have 480VAC in the panel. The control circuit voltage does not exceed 120
vac and that is what I am seeing in NFPA 79 in section 9.1.2.1. Maybe that is what you are saying? Or are you saying there has to be a separate panel for the higher voltages?
Regards,
Dave
Tim,
regards,
james
My control wiring would not be above 120 volts?
Recently we had a "Made in China"portable line installed Weiview TouchPanel MT8102iE, it has capability to connect CompactLogix and ControlLogix...
3,825
Hi all, we are assembling an industrial control panel which consists of 4 branch circuits supplied from panel feeder as follows: Panel feeder ...
5,215
Hi Experts, I have a S7 300 and ATC 1000. I wanna send 9 byte to LED panel through ATC 100. Plese help me ATC-1000...
5,500
When i load my client a[plication the following error is recorded in factorytalk view studio log Failed to load data server...
32
Sorry for my lack of knowledge, beginner here. Yesterday, we had a Pro-Face SP5000 HMI fail on us. The technician said that the HMI had the blue...
153