This is probably a basic question but need some info. We have several pairs of light curtains that the OSSD outputs go into the safety PLC and then the PLC sends the reset command to the L/C's. The curtians are reste hundreds of times a day and very intermittently we are getting a #1 output error on some of the curtains. The L/C manufacturer advised that the L/C needs to see a voltage level no higher than 1.3 volts above ground when the outputs are off or we could see the output error. They believe there is an issue with the grounding for the L/C's and advised to check and measure the quality of the ground. The curtains and the safety plc are fed from a separate 24vdc power supply by themselves. Not sure at this point how to measure the voltage on the ground wire. Can you advise the best way to go about this. Thx
There shouldn't be voltage drop on the ground. Thats why its called the ground.
Either make sure that all the grounds (0V) of the devices are all connected together or you will need to put interposing relays between them to isolate the signals from each other.
Also, check whether the common (ground, 0V) of either one
power supply is connected to earth, also check whether the PLC inputs/outputs have some link to earth. Then you may get a floating voltage between one of the ground(s) to earth.
BR
Stef.
Hi everyone! I'm working on the controls design of a semi-automatic pneumatic vertical press. The machine will consist of two double-acting...
1,778
Good Morning , I was thinking of using a Guardshield Safety Light Curtain on a palletizer. The light curtain I was thinking of using is a...
1,084
Hi, I'm new to the automation industry. While installing the light curtains what are the main factors to be taken care of? Is there any varying...
3,339
Good Evening , What type of output is coming from a Safety Light Curtain ? I took notice that normal relays will not work. I have all...
4,578
Good Afternoon, We have a light curtain system that momentarily see's that it is blocked. Is there an adjustment that you can delay ...
2,299