Load cell help

sharkyh2o

Member
Join Date
Dec 2013
Location
Snow Shoe
Posts
129
New to anilog signals. Using a 5-10vdc analog load cell not to exceed 15vdc straight to the input card on a micrologic 1400 processor and not getting the results i desire. At 10vdc each pound = 1. At 5vdc every 2 pounds = 1. At 15vdc each pound = 1.5, but i do not want to push the voltage limit. What would you recommend to be able to take the signal and be able to come within say .2 pounds
 
I am assuming that you mean you are using a load cell with 5-15VDC excitation. The load cell should then have a mV/V rating. If the mV/V rating is for example 2mV/V, then if you supply an excitation voltage of 10V, then the load cell will put out 20mV at max load. Unless you are using some kind of special input on the 1400, then you should be connecting the load cell to a signal conditioner that will amplify the load cell signal to something useful(0-10VDC for example).
 
sharkyh2o,

FROM YOUR earlier post.
"New to anilog signals. Using a 5-10vdc analog load cell not to exceed 15vdc straight to the input card on a micrologic 1400 processor and not getting the results i desire. At 10vdc each pound = 1. At 5vdc every 2 pounds = 1. At 15vdc each pound = 1.5, but i do not want to push the voltage limit. What would you recommend to be able to take the signal and be able to come within say .2 pounds"

please stay with the original posting. we will be more than glad to help.

regards,
james
 

Similar Topics

I have few questions regarding analog input. and i was wondering if you can direct me. i was able finally set my cards and connect my load cell...
Replies
3
Views
2,110
Hi everyone, so as i am still new to this. I will need help to confirm my connections load cell to my plc load cell will run on 10V max so that...
Replies
10
Views
2,650
New to anilog signals. Using a 5-10vdc analog load cell not to exceed 15vdc straight to the input card on a micrologic 1400 processor and not...
Replies
12
Views
3,214
I have to look into a new set up of a load cell fed into a HELM module (1769 series module with a Compactlogix). I spoke with HELM and gotten no...
Replies
2
Views
6,234
Dear All Friends I am trying to connect Siwarex U Load cell processor ( 2 Channel ) with Simatic S7 313 C CPU . But the SF ( System Failure )...
Replies
5
Views
5,711
Back
Top Bottom