Logix5000 tags importing to FactoryTalk Studio 5.1

tmechanic

Lifetime Supporting Member
Join Date
Aug 2005
Location
New Richmond, WI
Posts
40
I tried the trick of offline browsing by setting up a SerialDF1 connection, but I'm using Eth/IP for communications and the tags aren't working once I download the project to the Panelview 1250 plus.
Any suggestions?
 
An RSLinx Enterprise shortcut points to two different paths: one of them for Development and the other for Runtime.

Switch to the Runtime tab and check the Driver and path to the controller that you have configured there. That's the driver and path that the PanelView Plust terminal itself will use.

Post details; a screenshot would be ideal.
 
DINT as ASCII in PanelviewPlus 1250

Trying to read a DINT that's set up as ascii from a ControlLogix L72S to a Panelview Plus 1250, I either get the ASCII number i.e. 8080245670 or **** or ?????? . Any ideas? I'm using Factory Talk 5.1. I tried to load a screen shot from photobucket, but I kept getting a broken link.
 

Similar Topics

Hello, Can anyone tell me how to import the tags from my logix5000 project for use over into a factorytalk studio me program? I cant seem to...
Replies
16
Views
43,526
Hi! I am struck at this point to import 1000 tags from RSLogix5000 to Factory Talk View Studio. When I choose the factory talk view CSV file I...
Replies
9
Views
21,973
Hi everyone. I just got the new factorytalk view ME V5 software. I exported the Rs logix5000 tags inti a CSV file. In factorytalk I tried to...
Replies
18
Views
27,744
I want to read several disparate values of different data types from a second PLC with the MSG instruction via CIP Data Table Read message type...
Replies
11
Views
5,025
is there somewhere in logix5000 to track/record tags for a short time to see what is going on with a tag that i might not be able to see on my own...
Replies
1
Views
1,157
Back
Top Bottom