Looking for Solid State relay suggestions

rootboy

Lifetime Supporting Member
Join Date
Jan 2004
Location
Tennessee
Posts
1,375
Hi guys,

I'm going to replace our mercury-wetted relays with Solid State relays and I'm looking for advice on what you would use.

The current setup (what I would like to replace) is:

3 pole, 40 amp, 480 volt Mercury-wetted relays, and,
2 pole, 30 amp, 480 volt Mercury-wetted relays.

Both relays are controlled off of a GE Genius output block (there will be some leakage there) running at 110 VAC.


I've looked at HB Controls (www.hbcontrols.com), and they look impressive. Any other suggestions?


As always, thanks. :)
 
Don't Forget about Safety

You have several choices. Crydom is regarded as the best by many. I like Crouzet for a good balance of features and price.

The important part is safety. The typical failure mode of an SSR is shorted. You need the overtemp alarm connected to a non-solid state device. Mechanical contactor or mercury relay.

For true safety, a dedicated overtemp controller is needed.
If you only use one controller and depend on it's overtemp alarm, then wire the contactor to the normally open contacts (relay is energized in a non-alarm condition). In this mode, the controller's CPU must be running and 'happy' before it will energize the alarm relay and activate the contactor.
Configure open T/C for full scale and/or alarm.

A single controller configured this way will protect against shorted SSR and open thermocouple.
It will not protect against shorted thermocouple. Shorted T/C reads room temp. You need a second T/C and overtemp controller for that.
 
Thanks!

keithkyll said:
You have several choices. Crydom is regarded as the best by many. I like Crouzet for a good balance of features and price.QUOTE]

Thanks for the tip, and sorry about the late response, I was on vacation and forgot about this thread.

We've got a master contactor that will drop out the entire bank of relays if things get out of control, so we're good there.

The Crouzet relays look good, thanks again.
 

Similar Topics

Howdy All !!! Could someone throw up a simple circuit that will let me take a analog input signal and drive a solid state relay that will give a...
Replies
16
Views
14,956
Hello All, Please direct me to post to the right page. I am really new to PLC, and want to find a tutor who is familiar with Automation Direct's...
Replies
9
Views
312
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
Replies
2
Views
165
I have Allen Bradley plcs, I have had Circuit breakers and other automation equipment in the past. There's no solid buyers local. How much do you...
Replies
2
Views
238
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
Replies
1
Views
173