Just a quick question for you guys. When you talk about "Loop-Powered" for instrumentation, will this term implies that the voltage require to power the instrument in question will be supply by the analog card that the instrument is connected too. The analog card I'm using is 1746-NIO4I.
No the 1746-NIO4I does not supply power to the loop. You must use an external power supply. See picture below.
Mickey thank you for your reply. Can you point me to where you got that picture. I was trying to print it and it wouldn't come up correctly. How can I determine the specs of the power supply I need. The instrument is a Vaisala HMT120.
Loop powered usually means the device is passive, will not supply 4-20ma on its own.
There can be great confusion and many wiring mistakes on PLC analog input cards for these type of devices.
I have seen analog input cards that supply the loop power on one terminal, and the return from the instrument on an other terminal. These cards provide the path to the DC common to complete the circuit.
Other cards assume the loop power is provided externally from the card and the return from the instrument is connected to the card input and the card input common must be connected to the DC common to complete the circuit.
The signal for a 2 wire loop powered instruments always maxes out at 20.0mA. Although the signal maxes out at 20.0mA, various fault mode/upscale signalling runs at greater than 20.0mA, from 21.5mA up to about 22.5mA
So, I usually figure 25mA per 2 wire device for a 24Vdc power supply.
25mA is 0.6W at 24Vdc. That's almost any 24V DC power supply.
The smaller commercial power supplies are typically 15W (650mA) or 30W (1,300mA).
It's a whole different situation for 3 and 4 wire devices. Some take a large amount of power and their specs need to be checked for current draw.
I am connecting a 4-20mA signal from an RTD transmitter to an ABB ACH 550 drive. My sensor is an ACI RTD Freezer Transmitter with a range of...
1,757
Hi all I'm attempting to use a Phoenix Contact signal conditioner - the device accepts mV signals and converts this to a 4-20mA output. The...
3,147
Hello to all, I have an application where I have one transmitter 4-20 mA (loop powered) and I need to connect its current output to two AI...
2,947
Hello, We have a 4-20 mA loop powered level transmitter. Right next to it we would like to connect in series a Loop Powered LED bargraph...
2,321
I want to use an analog 4-20ma output sent to a loop powered digital process meter to display the temperature set point for an HVAC zone. This set...
8,081