Low Battery bit in CompactLogis L35E

ksa858

Member
Join Date
Jul 2014
Location
Danville
Posts
84
I am using the minor_fault_bit.10 low battery bit and programming it to a external indicator. My question is when the low battery bit comes on in the processor does it stay latched in until the battery is replaced? How does the fault reset itself?
 
The bit is set or reset based on the GSV execution. If you never execute the GSV then that bit never updates. If you attach the replacement battery and then the GSV is executed, your minor fault bit will be cleared.