M340 and TeSys T Modbus
grz3chubak
Sep 2020
Bytom
I create project where use PLC M340 and I need to communicate with TeSys T motor controller by Modbus RTU. In this project I have also ethernet module NOC0401 where I've add some modbus TCP devices and it works excellent. But to this module I can also add TeSys T with modbus RTU. I can set every parameter for RTU but NOC0401 also automatically assign IP address to RTU devices. I don't know if it will be work if I connect RTU devices to NOC0401 module which I configured it.
In attachment you can see configuration of modbus serial devices into NOC0401 ethernet module.
Can anybody help me if I can use it this way ?
The NOC0401 is Modbus TCP, it cannot communicate with a Modbus RTU slave without a Modbus TCP to RTU gateway, unless i am misunderstanding your question ?
you understood my question very well, just wondering why I can add and configure modbus RTU devices (TeSys T) in this NOC0401 module ? When I add some devices to this module, I can set if this is serial or TCP modbus...Screenshot in attach.
I am a little confused about this
I'm confused too ! I have no idea why it would do that. Have you got the correct DTM ?
For Modbus RTU you would need a NOM module, the NOC0401 quite clearly states its ethernet only in the manual:
Overview
The Ethernet communication module serves as the interface between a M340 PLC and other
Ethernet network devices by means of either the EtherNet/IP or the Modbus TCP communication
protocol
Yes, I have the newest DTM from Schneider site.
My M340 has Modbus RTU so I don't need any extension module, I only should use Read_var function which I didn't want to do but I don't think I have a choice o_O
You could put a gateway on the serial devices and still use the NOC, Schneider's own EGX (Link150) will do the job fine.
I was just about to say this. Isnt that the reason why you can place the modbus rtu version dtm in the dtm browser? Then the device ip must all be the same as the gateway but with different unit id?
Just thinking out loud here
I did wonder that but it's weird it lets you set it s Modbus SL as its effectively Modbus TCP, unless it needs to know its downstream of a gateway so it can handle timeouts etc.
Isn't EGX150 Modbus RTU over TCP gateway. So slave addresses is needed for communications.
Hello, I am new to the Schneider range of PLC's and im looking for some advice to communicating to 23 tesys U devices over modbus. I also have...
4,419
Hi, I am having issues finding how to communicate between a Tesys T LTMR27EFM and a Modicon M340. I have set up all of the ethernet settings on...
3,023
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
244
Hello all, I am wanting to update the system clock via NTP in the M580/M340. I'm aware that we are able to connect to a NTP in the controller...
144
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
318