mA signal to voltage input accuracy
naegely
May 2008
Florida
93
I have a very simple sytem w/ ML1000 analog processor (2 current analog inputs and 2 voltage analog inputs). The system has a pressure transmitter and temperature transmitter (both 4-20 mA) that are currently connected to the voltage inputs of the ML, with resistors across the terminals. This works OK, but I have the 2 current inputs available, and can easily move the instruments to them and modify the program. My question is, do you sacrifice any accuracy going to the voltage inputs through resistors vs. connecting to the current inputs?
Thanks for any info.
Rob
Yes you do. I had almost the same situation. An OEM peice of equipment came with an 1100 and a 4-20ma pressure transducer wired up to the voltage input with a resistor. I since switched it to a current input and found that it was far enough off for me to never do anything that way.
Rob,
The voltage in a circuit is different at different points, due to the resistance of the wire. Also, if your current-to-voltage conversion resistor is not an exact value (precision with low tolerance range) then you will have a built-in error. On the other hand, the current in a series circuit is the same at all points, so that the miliampere value sent by the transmitter is the same value read by the PLC.
I Disagree
MartiniRossy said
Yes you do.
I disagree. One way is just as accurate as the other. The 4-20 mA inputs have resistors across them and the voltage across the resistor is sensed by the input circuitry.
What may change is the accuracy of the resistor. You need to use a precision resistor or accurately measure the resistance of the resistor and use the actual resistance in the scaling calculation.
I know you didn't ask about this but if you are that concerned about accuracy I wouldn't use the ML1000. I've had problems with the embedded analog inputs. ML1200 would be better.
True, but the point is that the voltage across that resistor is probably NOT exactly the same as the voltage generated by the voltage signal transmitter. The signal transmitter has no way of sensing how much voltage drop is happening in the signal wire from transmitter to PLC. That is the voltage reduction due to the resistance of the wire, which is never 0, and may be large for long runs of wire.
Now, for a current signal, the current transmitter can measure the current and adjust as needed to match the current to the measured variable. This will be the same current as seen by the PLC input, because there is no "current drop" in the wiring.
If memory serves the ML1100 built in analog inputs are voltage only, 0-10 volts and are only 10-bit. So if you add a 500 ohm resistor, and use a 4-20mA instrument, then the range will be 2-10 volts, so you loose some resolution. If you buy an analog input expansion module, they have much higher resolution, can't remember if they are 12 or 16 bit cards.
Long story short, you get much better resolution with the add on analog inputs.
I thought the 1000 was digital only. Since he said he has 2 voltage inputs, I believe it is an 1100. I used my first 1100 just recently. I used the 2 voltage inputs with the resistors for 2 levels that didn't need tight tolerence. If given the choice though, I would use a mA input.
George
Vic is correct, provided you use a precision resistor across the module input there is no difference between Current or Voltage input. The A-D measures Voltage not current.
Roy
George
There are 3 models of the ML1000 that have analog. They each have 4 analog inputs and 1 analog output.
According to the manual, the ML1000 analog inputs have the same specs for the voltage and current inputs. Both are 16 bit. Voltage range is 0-10.5v, current is 0-21ma. So, it's pretty clear that a 500 ohm resistor on the voltage input will make it the same as the current input. You want a precision resistor just like the current inputs use.
Voltage signal vs. current signal from the transmitter is a whole different discussion. If you are going any distance at all, current is superior. If the transmitter is in the same panel and the wires are short, it's no big deal to use voltage.
Mellis, Yes, and I thought that Rob was proposing to use voltage transmitters instead of the present current transmitters. I was wrong. I see now that he was just debating whether to use the same current signals on a voltage or current input.
I know of and have used the pot to analog signal condtioners. I am looking for the opposite. I need to convert a 0-5V (or 0-10V, or 4-20MA) to...
2,846
I have a Allen Bradly Signal Conditioner card (931S-B1C6D-DC) hooked up to a strain gauge. The excitation voltage is 10V, the output is 4-20 ma...
2,049
Is there a device that will amplify a 1-2.2v signal to a 24v signal. I dont want to build a circuit.
3,587
I'm fairly new to the world of PLC's. So far I've managed to resolve the problems I've crossed but this one has me stumped. I've got a Rotork...
3,877
I have a vacuum instrument. The analog out is linear "with respect to the log of pressure". It is a 0-10v signal being sent to a Compactlogix IF8...
18
7,330