masked move ?
tboatman
Jul 2004
Whoever programed this micrologix used this masked move to delay a lift when it reached its upper limit (reed sw.) via a "thumb roll" pot.there is a cumulitive value in it that has to be re set every so often. what I would like to do is change it so when it makes the top limit it fires a tdr. this way the operator still has the capibility to vary the amount of delay. any help would be greatly appreciated.
MVM I:0.0 00FFh N7:0
FMUL N7:1 1 N7:2
RD N7:0 N7:1
MOV N7:2 T4:1.PRE
I find that i mostly used masked moves when there is an input card with 16 inputs (or more) and there is a thumbwheel switch (BCD) into 4 of the inputs. Masked move the inputs that are for the thumbwheel to a channel (register) where one can read the actual BCD value. Invaluable here. The other digital inputs can then be used normally in the program.
So Old Pfhaart could I just delete the rung for the masked move and use one of those inputs from the tdr ?
Not sure. What is a
"thumb roll" pot
Is it like a thumbwheel switch? If so, the masked move is probably moving the data from it to a channel or register so it can be utilised.
You are correct it goes to 4 inputs,and the way im seeing it each click of the wheel "00 thru 99" changes the resistence and the delay to the return Sol.
tboatman said:
FMUL N7:1 1 N7:2
MOV N7:2 T4:1.PRE
I think Bob is right here.
MVM I:0.0 00FFh N7:0 This is taking the lower 8 bits of the micrologix's input image and moving just those 8 bits to N7:0. The thumbwheel is probably wired to these inputs, with the right digit (0-9) wired to the first four and the left digit (10-90) wired the the second four.
0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
|________| |________|
0,10-90 0-9
MUL N7:0 1 N7:1 - This instruciton essentially copies the value in N7:0 to N7:1 but this is not the ideal way to do it in an AB. (Programmer must have been a Modicon programmer). A better way would have been MOV N7:0 N7:1. However, this rung is completely superfulous because its overwritten by the next rung, so I would just delete it.
FRD N7:0 N7:1 This converts the BCD number in N7:0 and puts in N7:1.
MOV N7:2 T4:1.PREThis moves the value set on the thumbwheel to the preset of timer T4:1.
It is not changing the resistance. The thumbwheel is an on/off device with four switches in it.
when the thumbwheel is on 0 the inputs are 0 0 0 0
when the thumbwheel is on 1 the inputs are 0 0 0 1
when the thumbwheel is on 2 the inputs are 0 0 1 0
when the thumbwheel is on 3 the inputs are 0 0 1 1
when the thumbwheel is on 4 the inputs are 0 1 0 0
when the thumbwheel is on 5 the inputs are 0 1 0 1
and so on.
0,10-90 0-9
If you delete the MUL rung (its actually MUL n7:0 n7:2) you'll need to change the last rung to MOV n7:1 t4:1.pre.
You're right, I mistyped that address.
Actually the best thing to do would be this:
FRD N7:0 T4:1.PRE
Unless there is a reason for the one scan delay in getting the TW value into the timer preset, but I can't imagine why there would need to be one.
Hello, I am using a UDT to track status from two different indexing lines that merge into one. Essentially, one indexing line is the part, and...
17
3,711
Hey I'm new to rs logic 5000 I have the basics but I'm getting confused with this mvm instruction. Can anybody bum it down for pls Thanx in advance
4,889
So I'm using a 1769-L35E. I'm trying to move two INTS through Masked Move Instructions to create a DINT together. I'm fairly new to this so...
6,780
can someone give me a plain english explaination of the MVM instruction and when to use it properly ...thank you ...
3,812
What Does The "masked Move" Function Do?
5,028