Hey Lancie,
I opened the links you posted, and tried the program out. Apparently, I plugged a wrong B3 data file in somewhere and I'm only executing the S:4 bit it seems. Some of the MOV and SQL and SQO instructions have been cut slightly off so that I can't tell exactly what the B3 words are, for exaple: B3:0 or B3:/0. Maybe that's where I messed up. What is your synopsis?
Thank you,
Jay
 
Syntax is important

I can't tell exactly what the B3 words are, for exaple: B3:0 or B3:/0.

You need to establish a baseline reference for discussing what you're doing in ladder. Part of this is correctly describing what you are seeing/trying to do.

In your post quoted above B3:0 is a valid address. B3:/0 is not. Although you might enter B3:/0 from the keyboard, RSLogix will insert the implied word number of zero and convert it to B3:0/0 when it builds the rung. In fact, you can enter a semicolon and it will convert that to a colon when the rung is built.

You can get a better understanding of these concepts by checking out appendix D (Programming instruction references), and E (Data file organization and addressing) of the SLC-500 instruction set reference.

http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1747-rm001_-en-p.pdf
 
Hey Lancie,
I opened the links you posted, and tried the program out. Apparently, I plugged a wrong B3 data file in somewhere and I'm only executing the S:4 bit it seems.
In my Post #8, the 8-rung "Sequenced Light Array R4.zip" file contains the LogixPro RSL program. If you download that, un-ZIP and run it with LogixPro, you will not have to wonder about B3:0. The only place B3:0 appears is in Rungs 3 and 5, and both are for the word "B3:0", nothing else.

Remember, this program starts out by generating and loading the 98 pseudo-random numbers into the Sequencer, so it requires 98 x 0.1 = 9.8 seconds before you see any flashing lights. Be patient!

Oh, you do have to set up an On/Off maintained-contact switch for Input I:1/0, and then switch to RUN mode and turn ON that switch. I think that you know how to do that.
 
Last edited:
Ahhhh, ok....
Obviously I missed that part of the link. My dang ADD must have been in overdrive that night Lancie. :oops: Thank you for your help sir.
 
In your post quoted above B3:0 is a valid address. B3:/0 is not. Although you might enter B3:/0 from the keyboard, RSLogix will insert the implied word number of zero and convert it to B3:0/0 when it builds the rung.

Doug, I apologize. I must have fat fingered the keyboard when I wrote the reply. It wasn't my intention to cause confusion. Thank you for your help sir.
It completely amazes me how total strangers on this forum are willing to help those in need. You guys are awesome!!
 
Hey Lancie,
I added the maintained-contact on/off switch and the program ran flawlessly. Thank you again for your help.
Jay
 
I added the maintained-contact on/off switch and the program ran flawlessly.
I have noticed an alarming trend in student programs - very few now bother to put in such boring details as Start and Stop buttons in their PLC logic. There are very few real-world machines that do not need some method to Start and Stop the equipment. The very first instruction to put into your student programs should always be a STOP pushbutton or switch. There are exceptions, such as the old traffic light program.
 

Similar Topics

Can anybody explain me how to type the following formula in a CPT block in Controllogix. The formula is the following 10^[((0.6*UA)/1000)-3] where...
Replies
2
Views
1,177
How would one come up with an average flow from the live GPM from the flow meter? I have the SCP set up and can watch the live GPM but I have...
Replies
15
Views
4,208
Hello Guys,Any one please tell me how to scale an analog sensor which is 0-10v and it has to be scaled to 0-8v or something using math...
Replies
7
Views
3,697
Okay I have read my book and my instructor hasn't addressed this issue as of yet. I am working on rslogix 500 and I was wonder if anyone would...
Replies
3
Views
2,870
I have an expression in a structured text routine of a Logix controller that looks more or less like the following: ResultInteger := Integer1 *...
Replies
13
Views
422
Back
Top Bottom