Mathe equation error
adam_lhadi
Feb 2022
algeria
59
HI
when using this piece of code
"1".Expenential_resault := ("1".Expenential_cof )**(("1".linear_Rows) -1); i get an error (Pic 1) how to fix it
the purpose is to get a resault of (+1 -1 +1 -1 +1........)
when i change the value manually it works great
"1".Expenential_resault := ("1".Expenential_cof )**(1 or 2 or 3... so on)
also this code gives me an error
"1".Expenential_resault := (-1)**(("1".linear_Rows) -1) using -1 gives an error but declaring a constant in data block with -1 value solve the problem ,so what's the diffrence
kind regards
if you change the "(3)" to "(3.0)" in the code that works it will probably fail.
try casting .linear_Rows as an integer. It might work.
The other option would be to simply toggle the sign of the result based on the result of of (.linear_Rows MOD 2). e.g. something like this:
Code:
"1".Expenential_resault := 1.0 - (2.0 * (("1".linear_Rows - 1) MOD 2.0));
Another option, that might work would be
Code:
"1".Expenential_resault := ("1".Expenential_cof) ** REAL_TO_INT("1".linear_Rows - 1));
Although I don't know offhand what the equivalent is in SCL for that REAL_TO_INT function.
qNaN. Possibly due to data type mismatch. Finding the problem is not easy.
Easier to use the #2 solution.
or
"1".Expenential_resault := "1".Expenential_resault * -1
If you attempt to use a hard coded negative number in a power operation you will get a compiler error 'negative base specified for power operation'
If you attempt to use a variable that is negative in a power operation you will get a run time error which you test for by checking the ENO variable in SCL.
Hi folks, I am upgrading a SLC to a ControlLogix platform. The goal of the project isn't simply to get the same program to run on different...
2,849
Hey All! Using the HSC:0 for an unwind. Not high speed or anything. 50 PPR at fastest 800 FPM.using this math pulse count per second / 50 the...
2,532
Any one know iso 1438 open channel Rectangular notch discharge equation
1,580
Hi all, Have a job where we're using peristaltic pumps to dose CL2 for wastewater, pretty standard 4-20mA flow pacing signal being used, no PID...
1,708
Hello, I've been told that this is the way i need to calculate airflow from a DP transmitter. I am far from a math genius and trying to find out...
3,075