Dear,
I am using in a pump control panel a relay connected to a high level switch that will stop the pump in case of high level in the receiving tank.
from the attached datasheet i can depict that the current needed for the level switch would be 0.08A at 240 VAC.
And considering an allowable 3% drop in voltage and for 1.5mm2 cable size, i got a value of 5118 meter which is 2559meter of cables run.
i really appreciate if you have any concern concerning the above. Any special requirements for the relay?
thank you!
Charbel
Dear Eric,
yes, true, i was considering in the calculation the maximum current that can be withdrawn.
thank you!
Charbel
0.08 Amps does not seem to be enough to energize a pump motor starter. Check the pull-in or inrush current for whatever device (contactor coil, relay, PLC Input) is connected to the 0.08-maximum level switch.
Dear lancie,
thank you for your reply, please see attached, the inrush power is 200 VA which is around 0.909 A at 220VAC, shall i take this value in my calculation considering that the maximum current that the level can whitstant is 0.08A.
thank you for your valuable advice,
Lancie is correct. You don't want that switch directly controlling your contactor. Even the holding current is at the limit of the switch's capacity. Have the switch energize a small interposing relay, and let that relay control your contactor.
-Eric
please find attached the selected interposing relay, what is the current withdrawn to be selected in the calculation of the cable length indicate above?
thanks a lot!
This relay will be OK. You just have to make sure the coil voltage will not drop bellow 176VAC according to specs.
Hello everyone, What's the difference between nominal sensing distance and maximum sensing distance in a diffuse photoelectric sensor ? in...
1,126
i am having a pull cord switch far from the PLC by X meters, i want to check if the signal will reach the PLC input module I am using 24 VDC...
19,623
What is the maximum distance I can run cat-5e or cable for rs323 I have a total of 4 SLC's in different locations I would like to establish...
3,529
What is a reference for the maximum jitter on the cpu of a controller for motion control? We have done some tests on an IPC with Codesys...
1,035
Hi PLCs.net! I was curious: How many axis can a B&R APC910 control? Is there a hard limit like certain AB controllers? I'm new to B&R, so would...
375