Dear,
I am using in a pump control panel a relay connected to a high level switch that will stop the pump in case of high level in the receiving tank.
from the attached datasheet i can depict that the current needed for the level switch would be 0.08A at 240 VAC.
And considering an allowable 3% drop in voltage and for 1.5mm2 cable size, i got a value of 5118 meter which is 2559meter of cables run.
i really appreciate if you have any concern concerning the above. Any special requirements for the relay?
thank you!
Charbel