Memory bits in Omron and SIEMENS
NskNSK
Jun 2016
Colombo
18
I am looking for addressing difference between Omron and SIEMENS.
In this Ladder netwoks has W10.00 address.This is a Omron ladder.
I want to know Omron W10.00 is equal to SIEMENS M10.0
If someone can explain all addressing deference between Omron and SIEMENS, I really appreciate.
Personally I believe M bits in Siemens are like duct tape and should only be used in trouble shooting and/or temp logic until you finalize your logic in a DB.
But if you are going to use the M bits just be aware that they are not all retentive. The CPUs I typically use are retentive from MB0 - MB16.
Ooo...really..
MB0-MB16 are retentive ? :eek:
How do you know that.
Can you give me some links about memory details in S7-300?
You can set this in the hardware config.
Specs of the 317F-2 PN/DP in this case:
Bit memory
Number, max : 4096 bytes
Retentivity, available : Yes (from MB 0 to MB 4095)
Retentivity, default : MB 0 to MB 15
Omron W bits are not retentive - H bits are.
Thanks BobB...
actually W or B bits in SIEMENS are not bit memory..W are word(16 bit) and B are byte(8 bit)
Am I correct?
If I use M0.0, Is it a retentive bit?
M0.0,M0.1,M0.2,M0.3..........M16.0,....M16.7
This all bits are retentive?
W is words and bits W0 is a word - W0.00 is bit 0 of W word 0 - W2.00 is bit 0 of W word 2. Free use with Omron - whatever you want. Some of the latest processors allow bit addressing of registers as well - do what you want. Siemens still insist on using bytes - I always find it hard when losing the freedom to do what you want when going away from Omron. Only byte use with Omron is with some remote I/O configuration - all else is words.
Talking about Omron - avoid Siemens like the plague these days - too hard - takes too much time - costs money and time. Siemens uses bytes for many areas - Omron uses words. I did not mention Siemens memory areas at all.
I might be understanding you wrong but with merkers you can use M,MB,MW,MD so i dont see your point.
Possibly referring to items like Siemens IO cards are addressed at the Byte level e.g. 0.0 - 0.7 and even if the next 8 bits are on the same card they are 1.0 - 1.7. But other manufactures would do it more as slot.point so theses addresses would be 0.00 - 0.15 or 0.00 - 0.31.
Newbie looking for help, please. When should one use memory bits versus memory words? Am I right in thinking a memory bit can be used to simply...
2,619
Hi, Is there a way to see all the bits in a variable or at a memory location in Unity Pro? For example, how do you look at all the bits in the...
1,885
Hello! I am using S7-1200 PLC 1212C AC/DC with configured Modbus TCP Server. I can already read/write Inputs/Outputs (Coils) and Memory Words...
3,015
I am upgrading a legacy HMI that was originally in Control View, then upgraded to RSView. There are a couple of dozen PLC bits being set by the...
3,449
Hi Hope someone can help(Newbie Question), I vaguely recollect reading somewhere that you can't or shouldn't use memory bits within an FB when...
37
11,199