Micro800 2085-OF4 - No 4-20mA Current Output
rbarbee
Jun 2016
Houston
I'm using an AB 2085-OF4 module for outputting process current control to various VFDs. When using this device, I have the channels configured for 0-20mA, but I am controlling the output to be between 4-20mA. I am using all 4 channels of the card. Images attached of the setup and PLC logic.
Channels 0, 1, and 3 don't seem to be outputting any current at all to the VFDs. Channel 2, however, does appear to be outputting valid 4-20mA when requested.
Using a process meter (Fluke 789), I attempt to measure the output of card and do not get an output on any channels (including the good one). I changed the output of the card to voltage and changed the wire over to the appropriate point and am able to read a valid output value.
I am really confused on why voltage, but not current, will work on this card. Is it a bad device? The diagnostic LED does not indicate any fault.
Is there anything else I could check or do to fix this?
When in current mode, what output voltage do you get for various current settings? If always > 5~10 V, then you need to check on the receiving end for proper loop resistance.
If it's useful to anyone else, this module still has a glitch whereby if the you remove the wire, it seems like the channel output gets disabled on the 4-20mA configuration. I don't know if this applies to the 0-10V as well.
To fix, I redownloaded the program. I don't know if there is a less invasive way to reset it. Rockwell really should fix this problem as this isn't typical behavior from what I've seen on the 1769 series of controllers.
Create a push button on the HMI to toggle a bit that will move 3848 into the control bit of that specific AO card, reset that back to 0 after 2 seconds. See attached picture.
Just ran across this issue. IS this really a thing? WOW. Is there a better way to fix this issue than a button on a screen?
My company built a small test machine using a Micro800 PLC and CCW software. We chose the Micro800 because the machine is very simple. We are...
147
Hi, Is there a way to set the IP of a micro dynamically, based on a variable value.?
161
Anyone use the newer 2080-L50E or L70E with 1734 Point IO yet? I have a customer asking for a setup and I have not found anyone that has done...
373
Is there a way to download the program to a Rockwell Micro810 without using the Rockwell CCW application?
726
Hi All, I am having trouble converting a real to string and keep it to 2 decimal places. I'm sure its a simple solution. Any help is appreciated
285