Micro800 PID issue, CV limits not working

Join Date
Mar 2014
Location
USA
Posts
16
Can someone tell me what i am doing wrong here? I have set the limits of the CV value for 5min and 60max. The output of the PID is not staying within the limits. here is a picture of the block:

CV.JPG
 
Just thought i would answer this for anyone else. The LimitCV function is if you want the min/max values to limit the CV.

I thought the limit CV was a separate limit, similar to .mo in rslogix. put a 1 in the LimitCV and it will use the limits
 