MicroLogix 1400 L32-BXBA

Christoph

Member
Join Date
Sep 2003
Location
Indiana
Posts
345
I have a project using the Micrologix 1400 L32BXBA.
i found in the manual which outputs are the Fast outputs. I know there are
a few Fast inputs as well, But I do not find a table like I did for the outputs.
Anyone know which ones are the Fast inputs or where I can find that info?
Thanks!
 
are fast inputs a thing? I thought that fast outputs were from those safety PLCs that could hit outputs at a much lower latency than other normal PLCs, but I didn't know that inputs could work the same way.
 
are fast inputs a thing? I thought that fast outputs were from those safety PLCs that could hit outputs at a much lower latency than other normal PLCs, but I didn't know that inputs could work the same way.


Yes, fast inputs are a thing.


For instance, with a 5069-IB16F input module, you can set up the 1st 8 inputs (2 groups of 4) as 30KHz counters. It works really well with flow meters. Also, a heck of a lot cheaper than an HSC module.
 

Similar Topics

Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
34
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
97
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
Replies
4
Views
224
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
306
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
652
Back
Top Bottom