Micrologix Analog 1762-IF4
tintorer
Oct 2006
Lima
Does anyone know if I can safely power up a 2 wire 4-20mA analog current loop transmitter, wired to a micrologix 1762-IF4 with a 24VDC power supply as described in the wiring specs, pub no. 1762-IN012A-EN-P pg. 11.
I have doubts, since the analog module is supposed to only be able to receive, according to the specs, not more than 10VDC.
The transmitter can work with a voltage range from 12VDC to 42VDC,
and the same terminals that power up the transmitter are the ones that carry the 4-20mA current signal that the analog module is supposed to receive as input, and I have a 24VDC power supply.
Any help would be appreciatted.
If you have the dip switches set for current, then running 4-20ma thru the
card will result in 5.5 volts (at 20ma) acrossed the card input.
The input impedence in current mode is 275ohms ( see page 19)
A simple series circuit.
Voltage Protection is + or - 30V
Current protection is + or - 32ma
Go for it!!
Hello All I have an application using a ML 1400 with 4 analog inputs and a 1762-IF4 expansion card with 4 analog inputs. I have 6 analog...
9,935
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
677
Hi all-- I need to create code in a Micrologix 1400 project that requires minimum, maximum and running average calculated values (Flows and...
17
3,749
Hello everyone.Am new in allen bradley configuration,i have a mini project to execute, i have wired my Micrologix 1400 for analog input signal of...
1,510
2,616