I am doing a special project with a Mitsubishi FX1S. This is the first time I have ever done anything with a Mits PLC and I am trying to get used to the GX Devloper FX software and I am having a bit of a problem. A very simple problem but I am banging my head against the wall.
I want to use X0 as a HSC. So according to the manual, I need to use counter C235. I want to count when M13 is on. According the the manual, I should just need a rung:
M13
|--| |----------(C235)--|
However the software will not let me put C235 in the coil. In fact, it will not let me put ANY C in the coil. I know I am missing something. Can anyone please point me in the correct direction here? Thanks!
Greg
Figured it out. I needed to enter it as:
|--| |---------(C235 K5000)--|
The manual is not very clear on requiring a K value for enabling a HSC.
The value does not need to be a K, but the value is the preset for the counter. So it is required that something is placed there as a preset. You can't code a counter or a timer without a preset.
Guys, Is the FX1S programming cable a an RS232 via the mini-din or does this require an RS422 or RS485 converter.
3,125
Hello, I'm trying to create a faceplate that features a bar where a real PLC tag is passed through the faceplate interface. I want to check the...
338
We're converting a SLC 5/05 to 1769 CompactLogix. The existing PLC is spread among two cabinets, with five racks total (last two racks being read...
1,652
Hi, Is there an easy way to limit the input tag by using min and max tags from the PLC? Thanks
1,294
Do people typically use both end limit sensors and configure soft limits for linear servo axes? I thought this was standard practice until one of...
5,814