Well according to the Citect Driver help file:
You can use serial communication to connect to Mitsubishi Melsec-FX2N CPUs via the MELSFX2N protocol. Being a point-to-point solution, the MELSFX2N protocol does not support multidrop installations. However, you can use one of the three connection methods outlined in the diagram below to communicate with the MELSEC -FX2N.
So you may need to think again about Citect and the way you have the network configured.
You can use serial communication to connect to Mitsubishi Melsec-FX2N CPUs via the MELSFX2N protocol. Being a point-to-point solution, the MELSFX2N protocol does not support multidrop installations. However, you can use one of the three connection methods outlined in the diagram below to communicate with the MELSEC -FX2N.
So you may need to think again about Citect and the way you have the network configured.