I need to display the temperature of a system on an E200 Screen from a 4-20mA PT. for 0-100 degrees.
What should be the offset & gain settings in the screen software
Also what should I set my controller value ranges to Lower & Upper?
Any help out there would be greatly appreciated.
It has been over 5 years since I did this and cannot remember.
I assume that the value when it is in the plc is from 0-4000
The controller value ranges (upper/lower) is that the calculator in e-designer you're talking about? It is just to calculate the gain and offset values.
So, if the values in the memory are 0(0degr.)- 4000(100 degr.), the values would be:
offset:0
gain 0,025
Hi francevendee,
I have attached an example with an A1S and the E200 terminal.
You only have to write the panel values and leave the controller value (leave the lower value to be 0).
Ex. I have the Temp value in registre "D0" signed 16bit
The controller value is lower = 0 and upper 32767.
The panel value = 0 and upper = 100
Tip. in the terminal you can use the [ALT] + 248 and it gives you the degree symbol [°].
Best regards
Dariusch
UPS....
You are so right NorthControl
the value must be from 0 - 4000 (if 11bit) for the controller value.
Sorry.
Has anyone tried to salvage equipment that has been under water in floods? I have had pretty good success cleaning with isopropanol and...
1,529
  • Poll
Hi Can we make a MITSUBISHI A1SCPU 25 PIN TO 9 pin RS232 cable for ourself? :scratch: Have anyone done so? Is it possible? umts007
3,522
I have a A1S38 Mitsubishi PLC i need to backup the program and then slightly modify it.I have GX developer 8 and got a sc09 lead off ebay. When...
3,463
Hi All I am programming a mitsubishi A1S plc and i need to have a time schedule set. Please could someone tell mee how to configure this. I know...
3,334
I work in a plant where there are about 12 of the older Mitsubishi PLCs, Series A1S. I need to loacate some older Software to Upload and Save the...
11,771