Hello everyone;
I have Mitsubishi PLC FX3U 32M in hydropower plant governor, an error message popped up when a technician was working on an Encoder connected to it for measuring a displacement, after pressing confirm on the error message, a counter started. after some days the PLC completely stopped all functions while there is no error indication on the plc.
Any expert kindly guide me how to tackle this error, it can not be reprogrammed because settings are done during commissioning for reliable operation.
Can I put the PLC back into normal operation without affecting the set parameters?
Providing the set parameters are either hard coded or in backed up registers then yes, I assume the error message was on programming i.e. GXDeveloper or GXWorks. providing you do not delete the program or download the Registers (Memory Main) then it should retain original settings, it would be a good idea to back up the registers & Bits that can be done by ticking the box on plc to pc transfer that is called device memory Main.
It would be helpful if you posted the actual error message.
Thank you Parky for providing useful information, today I got to know one of the attached module (2AD) is faulty, and may be due to persisting error the PLC program is locked. It shows all the set parameters, but doesn't execute any command. Hopefully I would be able to put it back into operation.
(I have attached error message),
Thanks!
WhatsApp Image 2023-11-14 at 16.48.19_f58d25c6.jpg WhatsApp Image 2023-11-14 at 15.51.41_28c5000d.jpg
Hi, I need know wath software is used for programing PLC Mitsubishi FX3u-32M? and were I can download this software?
13,885
Bonjour, Je n'ai pas de communication modbus RTU vis la configuration ci-dessus. J'ai essayé les deux mode ch1 et ch2 mais rien ne fonctionne...
182
hmi keeps saying "insufficient sensor failed" after the machine runs for 60 seconds. its a fx3u-48m PLC. The plc is not giving any errors or...
2,298
Hello All, I have been trolling through the Proface documentation to find an answer, but I read conflicting information. We have a...
3,957
Hi All, I am looking to install a Red Lion CR3000 HMI and connect it to a Mitsubishi FX3u 64M PLC via Serial. I cannot find confirmation on...
2,872