cottagewood
Hi, does anyone have experience with the Off Delay Long Timer function in GX works 3,
I need a PV greater than T#2147483ms
If I use Long Timer for the data type for PT I get a compile error
From the manual:
2.Delay time setting
The valid setting range of is T#1ms to T#2147483ms. Note that the valid setting range will be as follows by changing the timer limit setting using the engineering tool.
Minimum value
Identical to the long timer setting value [ms] in the timer limit setting.
Note that if the long timer setting value is smaller than 1ms, the minimum value will be 1ms.
Maximum value
The time satisfying the following condition is used.
Note that the maximum value is a value that can be included within the range of time type because the delay time setting value is of time type (32-bit value).
・Delay time setting value [ms] ≤ 2147483647 [ms] × Long timer setting value of in the timer limit setting [ms]
[Example]
・If the long timer setting value is 0.001ms: T#1ms to T#2147483ms
・If the long timer setting value is 1000ms: T#1000ms to T#2147483000ms
From the manual:
Minimum value
Maximum value
[Example]