pabeader Member P Join Date Oct 2006 Location elkhart Posts 18 Oct 26, 2006 #1 I notice that the documentation does not directly say if you can programm via the ethernet port on a ML 1100. So I am wondering, can I?
I notice that the documentation does not directly say if you can programm via the ethernet port on a ML 1100. So I am wondering, can I?
SAK-CO TECH Member S Join Date Dec 2002 Location Between Los Angeles and San Diego Posts 142 Oct 26, 2006 #2 Yes. Use the Ethernet Devices or the Ethernet / IP Devices driver in Rslinx. Regards, Chris
ndzied1 Lifetime Supporting Member Join Date Aug 2002 Location Chicago, Illinois Posts 2,857 Oct 26, 2006 #4 Just make sure you follow this tech note to set up RSLinx http://domino.automation.rockwell.com/applications/kb/RAKB.nsf/0/1340E017D9E50906C125707E0070EBCE?OpenDocument
Just make sure you follow this tech note to set up RSLinx http://domino.automation.rockwell.com/applications/kb/RAKB.nsf/0/1340E017D9E50906C125707E0070EBCE?OpenDocument
n_lev Member N Join Date Oct 2006 Location Melbourne Posts 105 Oct 26, 2006 #5 And make sure you have RSLinx of version not lower than 2.50
n_lev Member N Join Date Oct 2006 Location Melbourne Posts 105 Oct 27, 2006 #6 n_lev said: And make sure you have RSLinx of version not lower than 2.50 Click to expand... Earlier version would show your ML110 as unrecognized device with yellow question mark. Fortunately it still allows you to download, but I didn't try online edits with that.
n_lev said: And make sure you have RSLinx of version not lower than 2.50 Click to expand... Earlier version would show your ML110 as unrecognized device with yellow question mark. Fortunately it still allows you to download, but I didn't try online edits with that.
pabeader Member OP P Join Date Oct 2006 Location elkhart Posts 18 Oct 27, 2006 #7 Thanks for the info. You have been very helpful.