Hi all, I'm just getting ready to program an application for PID controling the temperature of thermal oil which is heated by 4 banks of heating elements. I have 8 contactors (2 per bank) switching the elements and one thermocouple for the PV. My question is how do I set up the output from the PID loop in the ML1400 as an on/off to one binary output instead of writing this value to an analog output. I have a number of PID applications running analog actuators fairly successfully but up to now none working with this type of setup.
Many thanks in advance
Dermot
Maybe you could try this:
0% output = 0 contactors active
12.5% output = 1 contactor active
25% output = 2 contactors
and so on...........
Select a desired time period for time proportioning your outputs. Then use the SCP instruction to scale the PID output to that time period and use that value for your on time.
For example, lets say that you choose one minute. Scale the PID control variable (0-16383) to 60 seconds. Now move that to the preset of a timer for your ON time. A second 60 second timer resets the first.
----------------+-PID-------------+
|PID FILE PD9:0|
|Process Var N7:0|
|Control Var N7:1|
----------------+-SCP-------------+
|Input N7:1|
|Input Min 0|
|Input Max 16383|
|Scaled Min 0|
|Scaled Max 6000|
|Output T4:0.PRE|
T4:1/DN
--]\[------+----+-TON-------------+
| |Timer T4:0|
| |Time Base 0.01|
| |Preset 0|
| |Accum 0|
|Timer T4:1|
|Time Base 0.01|
|Preset 60|
|Accum 0|
T4:0/TT HEAT_CONTACTOR
If you are using solid state contactors then choosing a 16.383 second time proportioning period (if appropriate for your process) and programming the timer with a millisecond time base and the preset word as the PID control variable has the advantage of simplicity.
----------------+-PID----------------+
|PID FILE PD9:0|
|Process Var N7:0|
|Control Var T4:0.PRE|
T4:1/DN
| |Timer T4:0|
| |Time Base 0.001|
| |Preset 0|
| |Accum 0|
|Timer T4:1|
|Time Base 0.001|
|Preset 16383|
|Accum 0|
If you have mechanical contactors you may need to include some anti-chatter logic.
Many thanks Alaric and Karsten for sol, I get the idea. Will post an update in a couple of weeks
Looking at your second example Alaric, would I be correct in assuming T4:1 time base should be 1.0 or PRE should be 6000 🤾
Stuck at home and need to adjust the CVH on a PID loop. I can build an AdvancedHMI HMI to read write the valeus, but I cannot VPN in. Is there...
1,666
Hi All... Using a AB MicroLogix 1400 and I am in need of a example of a working PID using an 1762-IF2OF2. I want to use an existing analog...
6,697
I'm trying to figure out if there is a relatively easy way to freeze the integrator in the Micrologix 1400. We've used some loop controllers that...
2,127
May be my question is too childish, but can i get all the answers please? For PID of ML1400, if I right loop update as 0.02 & time mode as STI...
4,770
Hi, I know it has probably been before posted before, but where can I get a sample program for a ML1400 or similar showing a working simple PID...
3,666