MM440 drive and F0070
userxyz
May 2002
any
2,768
I placed an MM440 as a slave of an S7 3152DP in a Profibusnetwork with 4 repeaters.
Sometimes the error F070 occurs on the MM440.
I checked the profibussignal with an oscilloscope and found this to be OK.
I already replaced the profibus module.
The telegram off time P2040 is 20ms as default.
In the diagnostic buffer of the S7 3152DP the error appears as slave with profibusadres 10 and missing etc.
Shoud increasing P2040 be of any help
Tnx
Problems with F0070
No One Ever had problems with the Fault F0070 on MM440's frequency Drives drom Siemens ?
Hi all, i m new to this forum. i recently had an assignment where the user wanted to copy parameters from Siemens Micromaster 440 using BOP. Help...
5,793
Sir, I have Siemens mm440 drive .which is using for conveyors .it's speed is controlling through pot (analog input 0-10 volt) But i am facing...
44
11,302
What is the meaning of F009 fault in Micro Master MM440 drive. We are not able find this fault in the operating Manual Mani
2,811
hi Iam using s7300plc communicate with mm440 drive. the communicate with each other but some data are not comming in hmi(current )iam sending the...
3,463
The Siemens manual shows the use of an electric pot as the appropiate connection for the analog voltage input but if you are using a PLC for you...
4,455