MODBUS and ML1400
sfindley
Jun 2010
Carrsville, VA
107
I am using a ML1400 to communicate via MODBUS RTU with 16 Powerlink G3 controllers. In the manual for the G3 controllers they state that there is another level of MODBUS Data called General Reference which is in the (6x) instead of the typical Coil (0x), Inputs (1x), etc. These controllers have some pretty useful data in this range and I was wondering if there was a way to use the MSG command to manipulate/access this data. The message setup screen does not give any option with (6x) included. I've searched the AB Knowledgebase and haven't been able to find anything refrencing this data range.
Any help would be greatly appreciated.
I think you might have hit the proverbial wall, here: MicroLogix 1400 controllers don't support the Modbus function codes necessary to read and write Extended Reference memory.
The Extended Reference memory type is described in the old Modicon PI-MBUS specification document (it's the one marked 'For Legacy Applications Only'): http://www.modbus.org/specs.php
Ken,
Thanks for the confirmation of what I believed. I was pretty sure that was the case, but was hoping someone with a lot more knowledge about AB than me might know a trick or something that I missed. Fortunately, I can still do what I have to do without the General Reference information...it just would have made for better HMI interaction.
Thanks for taking the time to answer my thread!
If I set up a ML1400 as a Modbus RTU slave, and click the extended files tickbox, then set up my files with 200 elements, will the Modbus...
1,079
I need to do 5 reads and 1 write on 2 devices. So that is 10 and 2 total. It seems I can't use indirect addressing with MG registers, which is...
3,130
I have a device that I am communicating with here that is using Modbus to store values from a gas analyzer and I want to transfer these to a PLC...
3,786
I am currently working on a project with an Epson Scara robot using an RC-90 controller communicating with a ML1400 Ser. B PLC. The robot...
4,024
I have an Allen-Bradley MicroLogix 1400, and have been working with it for a few months now and understand its basics pretty well. Up to now I've...
3,959