modbus connectivity in S7-300,CP341
falgunvasava
Jan 2009
gujarat
60
I need to read data from 3 Honeywell pid controllers which are used to control temperature which give modbus connectivity.
As i have found that CP341 with can used for modbus connection
but then it have RS232,RS422/RS485 and TTY three different types.
Can they all be used for modbus connectivity?
If someone says yes then how to decide which one to use.
what should i know about to Honeywell controller to decide that?
thanks in advance
Yes, all variants of CP341 can be used for modbus connectivity. To decide between RS232, RS422/RS485 and TTY you need to know the type of communication supported by the Honeywell PID controller. Look at the technical specs of the PID controller, it will specifiy what type of communication port it has and you need to use the same type of CP341 card.
Honeywell 1/4 DIN UDC line has an optional 2 wire, half duplex RS-485 Modbus RTU for digital communications. The printed circuit option card can be added to a UDC 2500, 3200, or 3500.
Almost any parameter is available via Modbus RTU.
Dan
Dear All Please help me on establishing connectivity between AT89C2051 and InTouch 10.1 on modbus ASCII. Your comments are most welcome. Manasi
2,229
Hello-time to pull the trigger on this project. I need to connect a Modbus RTU chiller to a Compactlogix PLC through ethernet to pass information...
2,291
Hi , I have a limited knowledge of MODBUS. I have been asked about connecting a device that needs to be able to listen to 2 way traffic between a...
1,566
Hello, I am connecting PC to Siemens S7-400 PLC via CP441 (modbus) & am facing problem while accessing the register memory area of Simantic...
1,426
Hi, Can anyone suggest me which prosoft module should I use in 1746 Chassis for getting connectivity with Modbus device? And how to configure the...
5,974