only done small bits with modbus 984
and there is no register from the manufacturer of the equipment
i have to be able to read and write to about 6 locations
the equipment is an electronics ballast for UV lamps
the existing PLC has failed and i need to install a new one
currently the items used are
Power, Voltage, Errors, Lamp KW input, Lamp Power, Run , Run Status
they manufacturer thinks the example in the photo tells me everything , but i just cant seem to figure it out - can anyone who knows hex addressing for modbus please assist ?
Modbus Register Maps - the armpit of technical documentation
Another example to prove my point.
I don't understand it either. It talks about 'bytes'. Modbus does not naturally send bytes - it sends and receives 16-bit 2-byte registers and strings of individual bits.
I personally love Modbus and use it all the time yet I frequently run into situtations like this where the documentation is unusable.
I wish you well in seeking more information.
This is where you go back to the manufacturer, tell them their doc is not helpful, and ask for examples from this page to be read using some 3d party Modbus client like Modscan32.
Are you sure this protocol is even Modbus and not a proprietary protocol? I've seen cases where people use the term "Modbus" to mean "communication protocol" because they don't know any better.
Can you share a link to the full documentation from your attached image?
From the sounds of it you have not managed to set up communication between the devices at all?
The photo seems to tell you how to control the device using existing communication, but nothing about how to set up the communication in the first place.
Perhaps what you need is detailed elsewhere in the manual.
It's Modbus RTU.
See the example on page 27 (attached and condensed in image below).
The new PLC will need to read all eight holding registers, starting at PDU address 0x100 (256 decimal). It may be that the PLC Modbus configuration will refer to that starting address as Modbus Address 257 (e.g. 40257 or 400257).
0x02 Server address (allows multiple servers on the same RS-485 multi-drop circuit)
0x03 Modbus command to Read Multiple Holding Registers.
0x01 0x00 (0x0100, 16-bit unsigned integer, MSB-first) PDU Address of first register
0x00 0x08 (0x0008, 16-bit unsigned integer, MSB-first) number of 16-bit registers to read
0x45 0xc3 (0xc345, 16-bit unsigned integer, LSB-first) CRC
My PLC Wont accept code like that
see photo
will aonly allow 0h type codes
is the plc confusing me or are the hex codes confusing me ?
could someone show me what i should have as the start address ?
You need put 100h only there. Read holding registers is same than 0x03 code. number is 1 to 8 depending how many registers you want to read.
see photo
What Lare said (0100h, possibly 0101h but since this is Modbus Hex addressing i.e. PDU addressing, the range is 0h to FFFEh it is almost certainly the former i.e. 0100h).
See here for Modbus RTU configuration on AutomationDirect CLICK PLC.
The 0x prefix convention is an alternative to the h suffix convention: if the PLC uses the h suffix convention then the 0x prefix is neither used nor needed.
Both conventions imply the digits are hexadecimal; I used 0x because that was what I saw in the ELC manual.
I agree with the above the holding registers are 0 to .. actual address 4000 to ..
below is a typical request for reading the holding registers (bytes)
01 slave Address
03 Function code (read holding registers)
01 Starting address hi (Hex 100)
00 Starting address lo
00 Quantity of registers hi (only reading 6 registers so hi byte is 0
06 Quantity of register lo
C4 Checksum lo
0B Checksum Hi
All the above are in Hex, it will depend on how your system treats the bytes it has been known that byte reversal is required and in some circumstances there can be a word offset so either 100h or 101h
The manual does not explain it too well but looking at it I certainly agree,
just an update for people - so i am going to site today to connect my laptop and use modscan and modsim to test and see what the equipment is doing
ill update later
Hello Everyone, I am using a raC_Opr_NetModbusTCPClient AOI module, as below,. So, I need some assistance to restrict in reducing the poling...
91
I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
68
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
327
120
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
288