Hello,

I need to connect a Modbus Plus PCI-85 Interface Adapter (416NHM30030A) to a Quantum Unity module (CPU 434 12A) but cannot find any pinout in the documentation of these equipements.

Can you please help me out? Maybe by checking the pins of a proprietary Modbus Plus cable?

Thanks in advance!
 
Modbus plus networks are usually made up with special connectors from schneider, a quick google gives these part numbers.

The Modbus Plus specification states that the following Modicon parts are to be used when wiring a Modbus plus network.

AS-MBKT-085: This connector is used for inline Modbus Plus device connections. If your module is going to be a drop in the middle of a Modbus Plus network, then use this Modicon connector.

MBKT-185: This connector is used for end point Modbus Plus device connections. If your module is going to be at the end of your Modbus Plus network, then use this Modicon connector.

HTH
 

Similar Topics

Some idiot cut the connector off my modbus + drop cable.....the end that goes onto the CPU (140-11302). Now I'm sitting with a 4 wires, Blue/White...
Replies
4
Views
6,875
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
11
Views
240
Hi Guys, I currently have a customer that has their Citect 6.10 SCADA system running on two WindowsXP SP2 PC's. They are connected to 10 remote...
Replies
2
Views
2,047
Does anyone know if it is possible on on these old Quantum 113/2 PLC's to use a currently established MB+ network to push a 4-20 value from PLC...
Replies
1
Views
1,408
Hello folks, I am working on testing some network issues on a PLC network developed in the early 90s. It is a Modicon Modbus/Modbus Plus network...
Replies
1
Views
2,239
Back
Top Bottom