MODBUS RTU 485 or RS232 (Multiple or single slave)
naturephoenix
Jan 2015
Vienn
181
Can someone confirm me:
If there is case with RS232 protocol there can be only 1 slave per 1 master on communication link
On RS485 can be 256 slaves bouned on 1 master?
On RS485 can be 256 slaves bound on 1 master?
Correct on RS232, its 1:1.
RS485 is 1:n but the limit without repeaters is 32 nodes, you can have addresses 1-256
Actually RS232 and RS485 aren’t protocols (Modbus RTU is) they are standards for serial communications. Because RS232 has a dedicated transmit and receive line it is sometimes perceived that it’s point to point only but it’s not. There are a lot of communication protocols that use RS232 in a multipoint format (including Modbus RTU). Having said that if it’s hardwired then you can’t do multipoint it has to go through something that separates the signals (usually radio modems). If the communication lines are hardwired and the application is multipoint then you do have to use RS485.
you can also use a splitter if it is hardwired. The one I have used the most is made by black box. You have the wire length limitation on rs232 but in my experience even at distances of a couple hundred feet rs232 will usually still work well. I wouldnt setup a new system in that way but if wire was already in place it is worth a shot.
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
232
I am trying to figure out some communication specifics for a Modbus RTU network that I will be integrating with and could use some help to make...
2,110
I'm getting no response from a device I'm trying to communicate to with a Beckhoff IPC. I'm not sure why it's not working. Attached are pictures...
642
Been trying for a while to get a flowmeter with Modbus RS485 comms to talk to my Redlion Graphite HMI. Cable has been checked 3 times all good...
875
HI guys: I am attaching several diagram from several sources, it seems to be that there is no such a wiring standard for modbus RS485 RTU. In some...
24
4,579