I am trying to control a Rockwell Powerflex 525 via Modbus RTU (RS485) using an ABB AC800M DCS controller, and am having some issues getting connected. The ABB controller has RS232C Modbus RTU comms, so I'm using an Automation Direct FA-ISOCON (RS232 - RS485 converter) to interface them. The PLC keeps reporting a lack of response from the slave when trying to connect.
After troubleshooting for a while, I ended up using the ModbusSlave software tool and a USB-RS485 converter to read the communication messages coming from the PLC, and it seems that the PLC is continuously sending modbus function code 08 to the drive, which the drive does not support. I was able to control the drive using the same USB-RS485 converter via PC, so I'm guessing this function code is the issue.
Anyone know of a way around this? Am I stuck using a different interface device or different communication card? Was hoping to use Modbus RTU since both devices have it built-in.
I have never used an ABB controller, so I don't know what serial port instructions or control are available. When I first saw this post, I thought about looking at CCW sample code for PF525 control over Modbus RTU. In a small bit of research, I came across this document, AC_800M_5.1_Communication_Protocols. The statement "Some slaves do not understand FC8. To avoid problems, set Poll Time to zero" on pages 85-86 leads me to think maybe that will stop the automatic polling for diagnostics, then it's up to you to control the communication in your code.
https://library.e.abb.com/public/6a203d3016146ec6c12578570041d62a/3BSE035982-510_-_en_AC_800M_5.1_Communication_Protocols.pdf
@5618: Super helpful, you may have just saved me from swapping to an ABB VFD. And I probably already read that document at least 5 times prior to having this issue šŸ™ƒ
Will give this a shot when on-site next and report back on the results.
Thanks!
Been trying for a while to get a flowmeter with Modbus RS485 comms to talk to my Redlion Graphite HMI. Cable has been checked 3 times all good...
871
Hi, I am constantly using S7 CB 1241 (RS485) Modbus comms to field devices, but these one was designed as a custom device. However I can see it...
3,045
Hi all, I have a Red Lion Display Station Plus that I am using to do protocol conversion from a EIP Micrologix 1400 to an air handling unit that...
5,196
Hello, I am wanting to get a Magelis to read holding registers from an IO device using FC04, but in testing it always seems to use FC03. The...
2,517
Hello, I'm trying to communicate with a Gree Chiller (x2) out of China. It has a Weintek Labs HMI that appears to have a modbus "server" (I...
3,579