ModBus RTU RS-485 communication using two differents connectors
Marcosbelgo
Jun 2015
Belo Horizonte
34
Hi friends, this is my first post in this forum.
I am Implementing an application that works like this:
I want use the RS-485 interface of MICROLOGIX 1400 communicating ModBus RTU with RS-485 interface of a Gateway (Modbus RTU/wirelles).
My question is:
If the RS-485 interface of Micrologix is a serial port DB-9 with many pins and the RS-485 interface of the gatway is just two connectors, is possible make the connetion?
Can I unplug the cables and just get the two cables from the communication and connect on the bournes of gatway? This work?
I attached the connetion schematic of AirGate-Modbus (from NOVUS manufacturer):
http://www.novus.com.br/downloads/Arquivos/v11x_c_manual_airgate-modbus_português_a4.pdf
You need a 1763-NC01 cable for RS485, this will give you the A/B (D0/D1), and common RS485 connections you seek.
And it is not DB-9 port that is Channel 2 you should use, but the channel 0 Comm port 0 - 8-pin mini DIN RS-232C/RS-485 connector. Use the 1763-nc01 as Epy said , it will be marked on the terminals what is what :)
Thanks,
I have another question:
Can I connect many PLC's in parallel and the last PLC connected to the gateway according the figure bellow?? If not, how do I do this Implementation?
rs-485 allows for this, the only issue maybe in the master radio, as to if it allows for point to multi-point, and multiple nodes.
This cable 1763-NC01 is very expensive 1763-NC01 OMG, I have 20 PLC's to communicate ..... The Micrologix 1400 do not communicate Modbus throug the serial port (DB-9) ????
Im not suire but isn't the 1763-nc01 just a pinout? You could build your own?
Anyways it's not that expensive?
Yes - but only via RS232 not RS485 as you are looking for. Then you're into adding RS232 - RS485 converters...relatively expensive with the numbers you're looking at.
List price for a 1763-NC01 is about £36 over here - not sure what you consider expensive?
Regards,
Rob
This is my question. If it is just pinout, why do not build my own? I searched for technical information aboult this cable and did not find anything. I would like to manufacture this cable...
It is always easier to use what the manufacturer make for us. In term of reliability and proffesionalism. It is really not that expensive, compare it to what all the PLC and cabinets cost it is really a small cost?
Regards,
Rob
Thanks Rob,
It is the same case of the cable, isn't the RS232 - RS485 converters just a pinout? I found very cheap converters for sale, which is the chance of I have problens with cheap converters??
I want start data acquisition from one of our plants and I am studying the possibilities. at first, how much can I make it cheaper is better. But, is sure that I have to make a professional work, not quick fix......
Regards,
Rob
Here in Brazil, it is more expensive.... more or less $80 ....
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
222
I am trying to figure out some communication specifics for a Modbus RTU network that I will be integrating with and could use some help to make...
2,093
I'm getting no response from a device I'm trying to communicate to with a Beckhoff IPC. I'm not sure why it's not working. Attached are pictures...
632
Been trying for a while to get a flowmeter with Modbus RS485 comms to talk to my Redlion Graphite HMI. Cable has been checked 3 times all good...
871
HI guys: I am attaching several diagram from several sources, it seems to be that there is no such a wiring standard for modbus RS485 RTU. In some...
24
4,530