Modicon 984-455 loses run & ready light
aaronhigg
Dec 2004
I have a Modicon 984-455 which is giving me problems. Without any reason or warngin it loses it run and ready light. To get it going again you have to cycle the power and start it again with the laptop. Sometimes it does it once a week sometimes it does it once a week, sometimes once a day, sometimes once an hour. I have checked the input power with a voltage recorder and it is constant. What else is there to check? After you lose the ready light you cannot connect with the laptop until you cycle the power. Then you get a stop code of 0200. Is there anyone that has encountered this problem before..... HELP!!!
Has anyone had this type of problem with recently purhcased Modicon 984's???
I do not recognize the processor 984-455. Is this the obsolete replacement unit that could be mounted in an old 484 chassis?
Does the processor lose it's memory (i.e. dim awarness) or does it only lock-up?
Rarely do CPUs fail intermittently. It sounds like you have a bad power supply, rack/chassis assembly, or an I/O card that is failing. I would start with investigating the power supply.
Hi
If your supply and rack are OK try clear the logic in plc ( remove the power off the plc and then remove the batery) and download your program again.
Regards
Andrzej
www.modbus.pl
stop code 0200
A few years back had intermittent 0200 stop code faults on a Modicon micro that was used on a Caterpillar Loader. Had to logon with laptop and start controller. Eventually found vibration causing bad ground on powersupply. Reterminated and problem went away. (At least that's what the technician told me.)
Brian.
Hi, Seeking consultation on an implementation matter, and have a question about Modicon Compact 984 communication through RS485: Three Modicon...
228
Hi I have a modicon 984 with proworx 32 that is scaling an analog input, and I need to adjust the scaling. I have new analog input values and %...
1,729
Hi, I am trying to get a machine started that was moved from one location to another. It has a Modicon 984-A131 PLC. I have Schneider Electric...
1,025
Dear Friends, I have Schneider PLC which is the world's first one Modicon i need software of Modicon PLC 984,it is known as...
968
I found the below logic in an old program. If I am reading the System Manual correctly, it appears that the UCTR will never count up to 10, since...
1,651