Modicon PLC(984-A145 CPU) program download

chanari

Member
Join Date
Dec 2004
Posts
6
Hello

I am trying to download PLC program from Modicon PLC(984-A145 CPU). I am using Modicon workshop software.

I am wondering what kind of cable do I have to use to get the communication working? Because I tried using a seriel cable(9 pin both ends) and I could not able to establish communication.

Thanks in advance.
 
A145. Thats a throw back. IIRC its a serial connection.

Does your serial cable have a cross over? Pin 2 must cross over to pin 3 between each end.
 
Remember- serial is not all alike. Is your cable straight thru? Using Modbus protocol your pinout should be:

9-pin female(computer) 9-pin male (984)
2------------------------3
3------------------------2
4------------------------6
5------------------------5
6------------------------4
7-8 7-8

Have this verfied and if it still won't go- give a shout.

Mike
 
I checked the cable specs and it is not cross over. I will try the cross over cable and see how it works out.

Thanks
 

Similar Topics

Hi, I am trying to get a machine started that was moved from one location to another. It has a Modicon 984-A131 PLC. I have Schneider Electric...
Replies
1
Views
1,023
Dear Friends, I have Schneider PLC which is the world's first one Modicon i need software of Modicon PLC 984,it is known as...
Replies
0
Views
968
I have a Modicon 984 and PLC Workshop for Modicon 32 Bit programming software from FasTrak Software Inc. Is there a way to load the program from...
Replies
6
Views
2,818
Hi all, I have been tasked with a project involving a Modicon E984-275 PLC. I have, unfortunately never used this type of PLC before and would...
Replies
8
Views
3,748
PLC Serial Connectivity Issue with a Modicon 984 and Modsoft 2.21 Hello all from PLCtalk.net, wondering if someone has any words of wisdom to...
Replies
1
Views
5,665
Back
Top Bottom