bluenoser337 Member Join Date Apr 2003 Location Nova Scotia Posts 391 Mar 27, 2012 #1 Not usually a Modicon person, but need to scale a sensor input (30009) on a Momentum. It is a 4-20mA signal but I'm not sure what the model# of the A/I module is. What is the range of these normally? (0-32767 or ??) Thanks!!
Not usually a Modicon person, but need to scale a sensor input (30009) on a Momentum. It is a 4-20mA signal but I'm not sure what the model# of the A/I module is. What is the range of these normally? (0-32767 or ??) Thanks!!
TConnolly Lifetime Supporting Member Join Date Apr 2005 Location Salt Lake City Posts 6,152 Mar 27, 2012 #2 Most of the Modicon stuff is 0-4095, but without specific module info I can't say for sure.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Mar 27, 2012 #3 See link to a manual below Chapters 6,7 8,9 10 http://www.google.com/url?sa=t&rct=...3PH9BQ&usg=AFQjCNFDjT_1e7zMx3pgsahit9obndL1Ag http://products.schneider-electric....s-infrastructure-and-oems/momentum-plc/#tab=2 Last edited: Mar 27, 2012
See link to a manual below Chapters 6,7 8,9 10 http://www.google.com/url?sa=t&rct=...3PH9BQ&usg=AFQjCNFDjT_1e7zMx3pgsahit9obndL1Ag http://products.schneider-electric....s-infrastructure-and-oems/momentum-plc/#tab=2
bluenoser337 Member OP Join Date Apr 2003 Location Nova Scotia Posts 391 Mar 28, 2012 #4 Thanks Mickey....that's a good book!!
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Mar 28, 2012 #5 bluenoser337 said: Thanks Mickey....that's a good book!! Click to expand... Your welcome.
(8{)} ( .) Lifetime Supporting Member Join Date Apr 2004 Location Israel Posts 625 Mar 29, 2012 #6 Just try to avoid Floating Point as much as possible in the Momentum. No FP processor. Good luck, (8{)} .) (Yosi)
Just try to avoid Floating Point as much as possible in the Momentum. No FP processor. Good luck, (8{)} .) (Yosi)