Outrage
Hi all,
I'm just wondering what you throughts are towards monitoring the status of the power supply to individual I/O cards on a rack. For instance on 32 way input cards I generally split the supply into 2 fuses.
The problems come when one of your fuses fails, how do you diagnose the failure?
In the past ive wired back a feed from each of the fuses into an input card, which gives you a concise alarm condition of individual fuses but depending on the number of I/O cards, you can start using up a lot of I/O for panel diagnostics. Ive also done it using a relay per fuse with the outputs of all the relays wired in series to give you a common healthy signal, which isn't as concise but still gives you a fault signal but conversely is an expensive solution.
What's your experience and solution for monitoring supplies?
Cheers,
Lee
Cheers,