Motor Data HP?
Tim
May 2002
Indiana
291
I got an AO Smith AC Motor and I'm trying to figure out what the HP is. I know there is a formula for figuring this but it seems like I'm missing something when I go figuring. The owner of the motor just wants to see if it would be okay to put it on a belt disc sander.
Here is what he says is on the motor.
RPM 3450
A 23.5
HZ 60
FR 184Z
Time Cont.
Thermally Protected
Type M
LKD Amps 120
He says its a single phase motor/ 220V.
If someone can give me an estimated HP rating, or somehow the way to figure the actual rating I would appreciate it.
Thank You.
Tim
Curious!
With all the other data provided, there must be a name plate on that motor and if so, does AO Smith not include the HP on the name plate along with all the other stuff? Seems to me most motor people do! Just an observation.
Randy,
According to him, there is no other information on the name plate.
Rs,
I kind of figured it would be around the 5 horse range. I used the formula in my UGLY's hand book and just estimated the EFF. I just wondered what to do because I didn't know the Eff or pf. I seen there were ways to figure these as well, but I was always missing some kind of data about the motor and got my math a little twisted and gave up.
Tim
I can relate to issues where the nameplate gets damaged and part can not be read. I meant to metion that 184 frame is also indicative of a 5 HP motor, the Z means that the shaft is special in some way...ie longer, bigger, may have threads etc.
FYI: Another rule of thumb pertains to the frame size, the center line shaft height from the bottom of the base is the first 2 number of the frame divided by 4...ie 184 frame divide 18 by 4 - 4.6 inches
I belive the motor is 4 HP which seems to be an oddball but that's what I come up with from my cheat sheet. Should have 30 amp duel element fuses.
BTW AO Smiths website leaves a LOT to be desired.
motor HP
RPM 3450 23.5A
Tim,
I'd get a look at myself and see what it says for phase. 23.5 Amps would put it at 7/12 HP 3phase at 208/230. I don't mean to confuse the issue, just wondering when someone else gives you the specs...as they say, been there, done that.
Bob
I have to agree with Waggs. 23.5 amps w/220 volts 3phase is dead nuts 7.5 HP. Also the fact that the rpm is 3450 also brings a LOT of suspesion about the motor being 3 phase. Ask the guy about how many wires are coming out of the motor.
Edit: The Frame (184) (open frame) also points to a 7.5 hp 3 phase motor.
Glad to see everyone's in agreement, NOT!... :D
Single Phase - I'd guess 5 HP (but only because 4 is just weird)
Three Phase - I'd guess 7½ HP
If I were a betting man, I'd put my money on Tim's motor being 3 phase, regardless of what 'the owner' says.
beerchug
-Eric
JesperMP said:
Unless this is supposed to be thermistors or Pt100's, then it is a thermoswitch connected in series with the leads to a single-phase motor.
??? We have quite a few 3 phase AO Smith motors (aka Centruy) with a thermoswitch. They're provided on a seperate pair, apart from the motor leads.
OK, but the wording "thermally protected" seems to mean that the motor has protection integral to itself.
Otherwise shouldnt it have been "capable of thermal protection via integral thermoswitch".
I have seen single-phase motors with a thermo-switch in series with the supply leads. But I guess that an integral bimetallic thermoswitch would never go to 23 A.
I made a few assumptions based on that statement. That this a home project so single phase would be what is available. My rule of thumb states 5 amps per HP at 230v 1 PH so I rounded it to 5HP.
The 184 frame could be either a 5HP or 7.5HP.
I couldnt make myself believe that people in an industrial environment would need to ask this question.
Hi The pump smart PS220 VFD has the ability to estimate pump flow based of pump characteristics and measured motor data. The calculations...
3,761
Trying to get a piece of equipment put back in to service. OLD VFD from this system has been scavenged so trying to add a new one to get it going...
2,887
Good Day All, Motor has the following Spec. 380-480V: 50Hz 0.2 kW 3,000 RPM 460V 60Hz 0.24 kW 3,600 RPM. This is a motor driving a...
1,785
Hello all, new to the community! I have been experiencing an intermittent servo fault on a Kinetix 5500 connected to a VPL motor. Fault code...
25,287
Hi We have one system where we use sinamics drive.The drive has been configured for 60Hz motor(1800rpm) and our supply frequency is 60Hz. Now due...
1,643