An FYI: The star delta method is not an American concept, it orginated in Europe and was in the US for compressors (hvac and air). To maybe clear the air about motor connections and how to determine connections when not marked I have prepared the following. This site limits text so I am dividing this into parts and creating a web page for it. For a better of view of this go to MY MOTOR WEBPAGE
Code:
<p align="center"><b><font size="4">Electric Motor Wire Marking & Connections</font></b></p>
<p align="left"><b><font size="3"><span style="background-color: #FFFF00">Single Phase
Connections:</span>
<u>(Three Phase--see below)</u><br>
</font><font size="2">Single
Voltage:                                                       </font></b></p>
<div align="center"><center>
<table border="1" width="20%">
  <tr>
    <td width="33%"><font size="2"><b>Rotation</b></font></td>
    <td width="36%"><font size="2"><b> L1</b></font></td>
    <td width="33%"><font size="2"><b>L2</b></font></td>
  </tr>
  <tr>
    <td width="33%"><font size="2"><b>CCW</b></font></td>
    <td width="36%"><font size="2"><b> 1,8</b></font></td>
    <td width="33%"><font size="2"><b>4,5</b></font></td>
  </tr>
  <tr>
    <td width="33%"><font size="2"><b>CW</b></font></td>
    <td width="36%"><font size="2"><b> 1,5</b></font></td>
    <td width="33%"><font size="2"><b>4,8</b></font></td>
  </tr>
</table>
</center></div>
</font><font size="2">Dual Voltage: (Main Winding Only)</font></b></p>
<table border="1" width="30%">
  <tr>
    <td width="20%"><font size="2"><b>Voltage</b></font></td>
    <td width="20%"><font size="2"><b>Rotation</b></font></td>
    <td width="20%"><font size="2"><b> L1</b></font></td>
    <td width="20%"><font size="2"><b> L2</b></font></td>
    <td width="20%"><font size="2"><b>  Join</b></font></td>
  </tr>
  <tr>
    <td width="20%"><font size="2"><b>High</b></font></td>
    <td width="20%"><font size="2"><b>CCW</b></font></td>
    <td width="20%"><font size="2"><b> 1</b></font></td>
    <td width="20%"><font size="2"><b> 4,5</b></font></td>
    <td width="20%"><font size="2"><b>2&3&8</b></font></td>
  </tr>
  <tr>
    <td width="20%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"> </td>
    <td width="20%"><font size="2"><b>CW</b></font></td>
    <td width="20%"><font size="2"><b> 4,8</b></font></td>
    <td width="20%"><font size="2"><b>2&3&5</b></font></td>
  </tr>
  <tr>
    <td width="20%"><font size="2"><b>Low</b></font></td>
    <td width="20%"><font size="2"><b>1,3,8</b></font></td>
    <td width="20%"><font size="2"><b>2,4,5</b></font></td>
    <td width="20%"><font size="2"><b>  -------</b></font></td>
  </tr>
  <tr>
    <td width="20%"><font size="2"><b>1,3,5</b></font></td>
    <td width="20%"><font size="2"><b>2,4,8</b></font></td>
  </tr>
</table>
</center></div>
<p align="left"><b><font size="4">
</font><font size="2">Dual Voltage: (Main & Auxiliary Winding)</font></b></p>
  <tr>
  </tr>
  <tr>
    <td width="20%"><b>1,8</b></td>
    <td width="20%"><b>4,5</b></td>
    <td width="20%"><b>2&3,6&7</b></td>
  </tr>
  <tr>
    <td width="20%"><b>1,5</b></td>
    <td width="20%"><b>4,8</b></td>
  </tr>
  <tr>
    <td width="20%"><b>1,3,6,8</b></td>
    <td width="20%"><b>2,4,5,7</b></td>
    <td width="20%"><b>  ---------</b></td>
  </tr>
  <tr>
    <td width="20%"><b>1,3,5,7</b></td>
    <td width="20%"><b>2,4,6,8</b></td>
  </tr>
</table>
</center></div>
<p align="left"><b>Single Phase Terminal Markings Identified By Color: <font size="1">(NEMA
Standards)</font><br>
        <font size="2">1-Blue
5-Black
P1-No color assigned<br>
2-White         6-No color
assigned       P2-Brown <br>
3-Orange      7-No color assigned <br>
4-Yellow        8-Red </font></b></p>
Application: I have two pumps, a 20 Hp and a 10Hp 3/ph 460v in the same conduit. The Vfd's are located in each mcc bucket. I have been getting...
6,228
I have a three phase 480 volt motor with six leads, but I can only identify the three sets of coils, unable to find the start and finish if that...
2,768
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
264
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
147
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...