Hey

Anyone who have managed to construct a motor valve control with Siemens logo and is willing to share?

What I mean is software controlling a motor valve depending on the outdoor and backtemperature in a building for example.

Kind regards
David Andersson
 
I think the Logo is the same as the Moeller easy relay and the AB Pico. If so, we use them all the time to control the level of tanks with a 4-20 MA input.


Most of these programmable relays are limited. Unless you get to the top line models (and why would you when you can get so much more with a PLC)you have a couple of analog iput (0-10VDC) and the rest digital. You usually don't have any analog output. Will your valve be proportional or OFF /ON?

If it's off / on, you can read the 4-20 by bridging a 500 ohm resister in the loop and reading a 2-10VDC input at the smart relay. You can then turn the valve off and on as required. If the Logo is not like the Moeller smart relay or your valve is proportional, sorry for wasting your time reading this information.
 

Similar Topics

Hi Experts Can anyone share with me the Function blocks for motor start stop valve control and level monitoring
Replies
10
Views
4,611
Hello All, I just finished programming some solenoid valves. I have to now program some Motor Operated Valves. The Controllogix PLC has 2 120VAC...
Replies
14
Views
5,552
Hi Folks, I am new in Cimplicity HMI.. and i have problem in calling a small windows for Motor/Valve "Start" Stop" "Auto" "Manual" command...
Replies
0
Views
4,601
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
280
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
149
Back
Top Bottom