I am reading Input status and Analog data from a Woodward device, my MSG blocks work but I had to place timers in my logic to make them all execute. I tried to set the first MSG with first pass or a bit at the end of the MSG blocks sequence, and use DN bits to execute the next MSG, Only one MSG would execute over and over without the timers to slow the logic...WHY???
Any ideas to clean this up a bit.
Thanks in advance.
Without seeing the logic I couldn't comment on how to change it, so ZIP the *.RSS file and post it (or at least the subroutine with the MSG instructions).
With Modbus, there's often an issue of inter-message delay, but we shouldn't look into that until we've seen the sequencing logic.
Remember that Modbus is a one-message-at-a-time protocol, unlike DF1 which can tell the difference between messages (because of the transaction sequence word). The MicroLogix doesn't buffer or stack Modbus master messages.
I use a method that Ken showed me some time ago. It used an add function each time a message is done (or errors). At the last message, use a move fuction instead of an add.
Im having some issues tracing bits through a message block. The bit originates in a PLC 5/80 (N246:10/0) and is messaged to a SLC 5/02. DH+ from...
1,736
Does anyone know why the MSG blocks stop working and sometimes show "waiting for que space" in the status and how to start the block working again...
3,147
I was wondering if someone could clarify / correct my understanding of MSG block on PLC5 / SLCs / ControlLogix platforms. MSG blocks are...
2,901
I have 4 Micrologix 1000's all connected together via 1761-net-aic's using DH-485. I want to use a MSG block to read one of the other PLC's or...
3,539
I have a question regarding MSG blocks and transferring information over ControlNet between Processors on a ControlNet Network. First off this is...
24,390