MSG Read SLC -> 5069 L320
twilliams
Apr 2020
Las Vegas
Hello. I have a new 5069 L320ER that I installed and I am trying to read and write data to an existing SLC5/05 via Ethernet.
They are both on the same network. I am attempting to use port A1 on the Compactlogix. I set the type as SLC typed Read, and the address as 3, xxx.xxx.xxx.xxx where xxx is the ip to the SLC5/05.. It goes to connection failed immediately. What am I missing?
Thank you in advance!
Is the SLC-5/05 more than about 20 years old ?
Early revisions didn't support the CIP protocol that ControlLogix does.
One quick way to find out is to use the EtherNet/IP driver in RSLinx Classic instead of the older Ethernet Devices driver. If the SLC shows up, then it's new enough to support CIP.
After a bit of trying, I can't seem to get anything on EtherNet/IP in RSLinx. It does not seem to like to cross subnets.
I have it working with another SLC5/05, and some PLC 5s but for whatever reason I cannot directly communicate between these two. I was able to read the SLC5/05 with an old PLC5 40E, then read the PLC5 from the new Contrologix. I don't understand why I cannot talk directly to the SLC.
Even when reading the SLC from the PLC5, I had to use a PLC5 typed read.
Thank you for your help. After diving in further and trying many things including messaging to and from other SLC5/05s and trying from another ControlLogx, it appears this is an old SLC that cannot communicate via modern CIP message standards.
I was able to work around this issue using a temp fix by message read and write from a PLC5 40E, and then to my new CompactLogix.
Thanks for the update !
I slacked off a little on you by only describing the RSLinx driver method for figuring out the communications ability of an old SLC-5/05.
Because I'm familiar with the controllers, I would have looked at the Device Properties in RSLinx and looked for an "Firmware Revision Number" of FRN5 or higher. Similar information can be seen in the embedded Web pages for the controllers and in the Controller section of RSLogix 500.
The other confirming method is to test the controller's ability to open a TCP socket on a specific port. I use TCPing because I've been using it for ages and it always gives me the correct result. 20-year-old SLC-5/05's without CIP support only open a TCP connection on Port 2222, while "modern" SLCs will open a connection on both 2222 and 44818.
Code:
tcping [ip address] 2222       Legacy A-B Client-Server protocol
tcping [ip address] 44818      CIP protocol over EtherNet/IP
Good Evening , I'm finally understanding a MSG instruction a little better. My question is , I'm using a MSG read in a CompactLogix to see...
1,909
I'm getting error 16#0008, unsupported service request in my MSG config. I have a CompactLogix w/L33ER. In slot 10 I have a Prosoft MVI-DFCM. I am...
4,825
Hello, New to the forum here, and to the controls industry. I am trying to do the following: Read and Write to a 5204-DFNT-PDPMV1 ProLinx...
1,889
I programmed a couple of MSG instruction for a PLC5/80E to write and read data to a SLC 5/05 thru an Ethernet network on non-continuous mode. It...
2,498
I'm trying to MSG from a SLC 5/05 to read a single INT from a PLC-5. I can't for the life of me get it to work! SLC Ch1 Config RsLinx...
5,755