Hello All
I'm trying to write a Dint from a Compact Logix 5069-L306ER and a 2080-LC20-20AWB.
I was able to get a CIP Data Table Read to function as expected.
However I am unable to get a CIP Data Table Write to work.
I'm seeing error
16#0005
Error Test:Class or instance not supported
Path is 3,192.168.1.12
Not sure what I'm missing and I'm not finding much information online.
I'd appreciate any advice or suggestions.
Mrdegold
After I posted this I walked away. Which is when I came up with checking that my destination address in the Micro 820 was set as a Global Variable.
So I created a New Dint Tag in the Micro 820 made sure it was a
Global Variable.
Bingo MSG Write started working as exected.
Sorry for the trouble
mrdegold
Thanks for the followup !
The target tag's folder/scope is a classic mistake, which I have made myself numerous times.
The Ethernet has 3 pieces of PLC5 processors (PLC5-40E), for easy explanations, we name A,B and C. All pings are OK and RSLogix5 can connect all...
4,931
Hi All. I can write an N7 value to a modbus register in an Automation Direct Servo but I can't read a holding register to an N7 address. I've...
1,906
Hello All, I've got a Compactlogix (v30.11) communicating to a SLC 5/04 over ethernet (CL side) through a AN-X2-AB-DHRIO module to DH+ (SLC...
2,336
Got a trouble call from a customer this AM that one of the compressor systems is getting its setpoint overwritten and mode (local/remote)...
2,099
Hello, New to the forum here, and to the controls industry. I am trying to do the following: Read and Write to a 5204-DFNT-PDPMV1 ProLinx...
1,892