My Rslogix stays stuck on Splash Screen

any of the Major software revision should be able to go online as long as the major revision matches.

While generally true, there is a specific compatibility issue with 20.03 (see the technote MikeyN linked). v20.04 or v20.05 should be able to go online with anything however.

There was a similar issue with v21 as well.
 
This is worth repeating, (AFAIK), ONLY ONE MAJOR version can exist on a PC at one time.

- If you install 20.0X followed by 20.0Y then 20.0Y is what you end up with. That's my understanding...

My project is 20.013. I installed 20.01.01 to run it and it would error out on opening. I trashed 20.03 and installed 20.04 and, Eureka!
 
While generally true, there is a specific compatibility issue with 20.03 (see the technote MikeyN linked). v20.04 or v20.05 should be able to go online with anything however.

There was a similar issue with v21 as well.

Correct but my statement is also true. The Technote is referring to the offline ACD file compatibility and the V20.03/01 issue is with the programming software.

It's still true that any of the V20.xx Logix5000 can go online with any of the V20.xx Firmware revision.

Just want to be clear.
 

Similar Topics

Hello, I am trying to read a barcode scanner input using a cognex dataman 280 barcode reader, store it another string, the compare with another...
Replies
1
Views
62
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
98
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
171
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
Replies
3
Views
196
Back
Top Bottom