Need help in drives & motors

Nelliyan

Member
Join Date
Sep 2011
Location
*******
Posts
90
Hi all,

I need some basic information in motors & drives

I tried studying but it confusing me a lot

what is the need for drive in motor operations , why cant the motors run in direct AC supply or DC supply...What is the advantage

The basic many will say to control the speed of motor , if we use voltage regulator by varying the 230 we can reduce speed & viceversa.

Pls give me a direct answer
\
Thanks & Regards,
Nelliyan.G
 
the main purpose for drive is to regulate torque and/or speed. V/f regulation is a part of VFD but VFD is os much more, it can regulate current, it has built-in PID, protections aginast overloads, overcurrent, torque control, and many other useful possibility.

direct online start of AC motor, and since most of them are delta connected, draw a starting current up to 9x nominal, and that can be a big stress on power supply, cables, and protection equipment, especially at high current ratings, and where constant start stops are required.
 
Variable Frequency Drives (VFDs) provide speed control for a standard induction "squirrel cage" motor. This type of motor is the most economical for a given horsepower, and is simple and reliable. For most other types of control you need a special motor of some sort.

You can't vary the speed of a standard three phase induction motor by varying voltage.

The advantages of drives depend on the load and the application. For many applications energy savings is the main justification for using a VFD instead of across the line operation. For other applications process control is the most important factor. In other cases, as stated above, reducing starting current and stresses is important.
 
Prior to Variable Freq Drive - in industry
90% of motors were 3 phase induction. They could run at only one speed - with a few exceptions which also had control issues. They were started DOL and reversed by stopping and then restart. Starting current in general was 4 to 9 times running current.

IF variable speed was needed - in the vast majority - DC motors were used. THe most common used was shunt. Series and compound were also used. Shunt was popular because it had only one field to control and was easy to control on Ward Leonard type drive systems. These varied the armature voltage to control speed and direction. They also controlled dynamic braking to allow for quick motor braking. Shunt field voltage and current was commonly supplied from an independent power supply and generally left alone. In a steel mill the main "blooming mill" drive motor was circa 5,000 HP.
DC equipment was quite labor intensive in that it required a lot of labor to do brush and commutator maintenance, controller maintenance including changing contact tips and voltage dropping resistors.

Nowadays with the VFD the whole picture has changed and many places are changing from DC drive to AC drive.

The reasons in priority - which of course is subject to argument
1. Lowered maintenance
2. Speed control of equipment
3. Lowered starting current
4. Dynamic braking
5. Energy savings when able to drive centrifugal pumps and blowers at reduced speed.

Dan Bentler
 
It sounds to me like the OP needs to focus on studying how a three phase induction motor works. Only after that is fully understood will VFD technology make any sense.
 

Similar Topics

Hello Forum, Having issues adding a module to the project. A 525 Powerflex drive when add the module rslogix program gives a fatal error and...
Replies
3
Views
1,993
Hi all i need to understand the parameters for this type of drives to establish the control for srvo motor by normal terminal and also by the...
Replies
2
Views
1,735
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
50
I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
347
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
173
Back
Top Bottom