need help
hi all
I have plc omron (cpu CQM1H)
I used with a system many Digital inputs many Digital & analog outputs
one Digital output module has Dameged I replace with a new one
after that the analog output which control the frequncy of many inverters was STOP & this is the problem.
Did you replace the digital output module with the exact same type?
Did you put the output module in the exact same order?
If not, the addressing is different for the whole system.
thanks Jay Anthony
but I replace the digital output module with the exact same type
&I put the output module in the exact same order.
Maybe the PLC is in PROGRAM mode
Dear Sameh,
I was reading the operation manual of CQM1H (catalog no. W363-E1-2), Section 6 describe the DIP switch settings of CQM1 PLC. I found out that there is DIP switch setting (pin 7) that determine the operation mode of CQM1 upon power up of the PLC. base on the manual, if no device was connected to the PLC (for example hand-held programming terminal) and pin 7 is off on power up the PLC will be in PROGRAM mode but if pin 7 is on, on power up the PLC will be in RUN mode.
If the PLC is in PROGRAM all outputs are disabled.
see the link below for your reference
http://www.trascon.ru/dynamic/managers/manage_6/files/w363e1-2.pdf
Jay Anthony
I am using CQM1H-CPU51
Vicente Jasareno
the pin7 is on & all machine is runing , the analog outputs are not effective & it's power led is on.
thanks for the PDF file I read it.
Sleepy Wombat
the system is running
thank's all .
I have a question about SET instruction in Cx-programmer. When condition goes true it is supposed to give value 1. But, my controller is giving 0...
24
2,304
Hi, I don't have any formal education background with PLC. I am learning PLC by myself. I have CJ2M CPU34 unit and CJ1W-DA021 unit. I would...
1,250
Hey all, I am working on this new project where i am devloping hmi in cx desiner , i have one question if i want a screen which only shows on...
1,733
hello guys I'm having problem in pid in Omron cp1l plc I have program . I'm getting alarm when I execute pid
2,824
Good day all, Newbie here so I'm practising my posting skills. I have a problem with one of the Omron C200HG PLC''s in our plant. This particular...
1,479