Need simple setpoint device for room temp
LMDAVE
Oct 2006
New Orleans, LA
50
I'm surprise what I'm looking for is giving me trouble, but it's basically a device like a thermostat to feed the setpoint to a PLC without the need of sensing temperature.
I already have a Vaisala transmitter monitoring temp and humidity in the room. The user just wants to set the setpoint.
I just want a simple LED device with an up and down buttons that basically outputs 4-20mA of the number selected. No ON/OFF relays, no input device, just a simple setpoint control panel, so they can set the room temp.
Anything I come across is way too complex for this application.
I need a value to set the setpoint, not a dig input to say I need cooling. Its just a basic PID controlling room temp from the VAISALA to a johnson controller. I just want to be able to set the setpoint from a remote location without having an HMI station.
What kind of PLC? Is the PID control done in the PLC? There are a bunch of ways to do it.
The setpoint could be related to an analog input, something like a potentiometer feeding into a DC volt input. Just relate the input to a scaled integer register going to the PID control block. How you will display the setpoint could be a process voltmeter that can be scaled the same as what you would do in the PLC. You would need a power source like 10vdc, a pot something like 5 or 10k ohms, a digital scalable volt meter that needs a power source (24vdc, 120vac?). I would look at a small HMI that could be the same cost without much messing around.
Yes, that's all I want is like a potentiometer setting the setpoint but it has to be digital, not a pot. The PID is already set, the transmitter is the PV, the controller has a setpoint already. I just want to use one of my analog inputs to have a remote device set the setpoint.
something that would look like this: (the omega unit only has relay outputs)
but I dont' want temp input on it, I just want it to be able to adjust a number (say 0-100), and have that number scaled 4-20ma and sent to an analog input. Just a simple LED device to set a value to a PLC.
http://******/1yT9xbm
Beka has device like that or you can build your own with couple resistors, pot and display :)
Boneless, I think those are display unit reading a value.
RDS, that is close since it's used to control speed I could have made it for setpoint, but the connetions looking dedicated for a VFD.
I decided to go with what I used in the past for this. It senses Temp and humidity and allows you to set the setpoint for each, and outputs all four: temp value, humidity value, temp setpoint, and humidity tempoint. I really just wanted to do a temp setpoint and that's it, but I'll use this since it is going in a clean room enviornment anyway.
http://www.veris.com/Item/HT2NAS0.aspx
You can set an analogue output on them to.
The piece you picked is pretty pricey as well, why not go with a small HMI?
Because the VAISALA temp humidity transmitter I was going to have in that room is well over $1000, I'm going to drop installing that transmitter and use this VERIS for everything now. So, actually I'm saving money.
Get google to search for XTR105.
Use one to get a temperature to 4/20 mA
use another one also to read same temperature, however now the Pt100 is in a wetted sock this will give you the wet bulb temperature (with some calcs you can get the RH.
and use a 3 to have a potmeter set
when using a potmeter of 25 ohms and a resistor of 100 ohms
you will have a homemade thermostat for around 25 euro (and still very precise better as 0.1 C.
1000 euro for a thing i can make for 50 bucks.
I've been working on replacing some PLCs for my clarifiers and I've got the PLCs and the program is written looks like it will work well thanks to...
2,317
Hi, I am currently working on a little project and I am wanting to control a fans speed with some PLC digital outputs / anolog output but unsure...
3,443
Question 1: I am still new to this - I also might be asking for too much. - but i need help using Ladder Logic to run (rod style actuator motor)...
1,677
Hi! I am desperately looking for some simple sample programs to learn Step7. Something like the manual of Working with Step7...
52
20,333
My skills haven't encompassed this to make me confident, hoping for some expert guidance. Scenario... I have recently put a wireless router into...
5,272