I am troubleshooting an actuator which is not responding to the plc code. The range in the channel of the Allen Bradley 1756-OF8 Analog card is set to 0-20 mA. The range is set from 4mA (1638 engineering units) to 20mA (8191 engineering units). When I signal to 1638(4mA), I get a reading of 2mA. I then set it to 8191(20mA) and got a reading of -2.5mA. Then I set the value to 0 engineering units which is outside of the range and I got a reading of 4mA. Does anyone know where I should go from here?
YaydonElcock Welcome
I just set the module in a test program
And the way to set that up is Rang 0 Ma-20 Ma as you have done
But scaling :
The default engineering units as percentage
High Signal would be 20.00 Ma = 100.000%
Low Signal would be 4.00 Ma = 0.0 %
That should give you what you want
You need to set each channel separately
I found no provision to do other engineering units
Hi everyone, I am working with micro850, a proximity sensor (FOTEK, PL-05P) and a 3DOF serial arm robot. I use MC_MoveRelative to control the...
62
I have 3 koyo PLC's in series. The 1st and 3rd are reporting values correctly but the 2nd is reporting negative values. The values in the PLC and...
1,419
Hi, I am connecting an Autonics make stepper driver type, MD5-ND14 to a Kinco PLC (K205 series) this has a sourcing output which cannot be...
1,116
Hello. I am trying to figure out how to setup a PID in Control Logix 1769 Controller in a way that it would control a drive speed by sending...
1,622
I'm loading bulk tankers with dry powder using a 1769-L33ER. Product is fed through gates, and close to the end of the load the system jogs...
3,091