no communication between contrologix and PV+
LBato
Nov 2012
b.fr
Hello everybody, I have no communication between my controllogix5561 and my panelview+ 1500.
I can download program in my contrologix and my panel.But I don't have communication...
I have make a cable 2711-NC13 for the communication,but the LED "RS232" is always "off" when I run the application (.mer).
I think I have setting problem, beacause in panelview+ "setting and communication" parameter I have no device(and no shortcut in setting of application..) !
In rsview32 (CPR7), in rslinx enterprise->communication setup I have : look attached files. maybe a problem with local/target setting?
I have make address 2 in the controllogix program, and address 1 in panelview setting.
thanx you for hepl. :)
Both your local (your local design computer) and target (Panelview) paths should point to the Control Logix PLC.
Then when downloading the runtime, choose over-write comm's settings.
I have a paths, no? beacause I have address "2" for the controllogix. maybe I don't understand your message.
It looks like your paths have not been set correctly, or they have not been downloaded to the Panelview correctly.
When first setting a shortcut, or when changing a shortcut, you need to check the box that says "Replace communication settings" when transferring the runtime application.
See attached picture.
Thanx you brendan, Yes I have not "apply" the shortcut to the controllogix.
I need to apply the shortcut, after I copy "local" to "target" and download to the panel.
Now I have the config and shortcut in the panelview! thanx you.
Hi everyone, is there anyway to read more than just one generic ethernet module with the same IP address in RSLOGIX5000? i just can read one...
1,248
hello i need some information about communication ge fanuc 90-30 and controllogix in ethernet ip?? Somebody can help me or send me some...
4,842
3,902
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
242
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
65